AC Hi pot Test

AC Hi pot Test

AC Hi pot Test

(OP)
we are doing AC hiPot test for Medium voltsge cables,the volateg level is 4.16 kV & 13.8 KV .for 4.16 KV , the  isulation withstand level for 4.16 Kv is 6/10 Kv ,so we can inject 3 times Uo (ie 18kv) FOR 1 hOUR. I am under the impression that this is as per VDE standard , can somebody confirm this

RE: AC Hi pot Test

You need to follow manufacturer's recommendations.  IEEE no longer recommends hi-pot testing for MV cables, IIRC.

Search this forum.  This has been discussed previously.  

RE: AC Hi pot Test

I remember IEEE has reduced discussion of dc hi-pot of cables (if memory serves me right, it's still listed in but not necessarily recommended)

I didn't realize the same applied to ac hi-pot. Does it?

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: AC Hi pot Test

AC hipot is still OK, but a 60Hz an AC hipot needs a ton of power to charge a MV cable of any signifigant lengh, thats why VLF is used instead of power frequency for AC cable hipotting.

I will need to double check your testing specs Monday but sounds right to me. (Not sure an hour is necessary, you dont mean 1 hour per phase do you?)

RE: AC Hi pot Test

My bad - I missed the ac reference.   

RE: AC Hi pot Test

(OP)
We insert 0.1hz frequency, all the Phases are joined together & for 4.16 KV cable (insulation level 6/10 KV)we give 3Uo ie 18KV for 1 hour, the leakage current in one sample we got 3.1mA.This particular method was advised by the Testing company.so the voltage which we are giving is given to three phases simultaneoulsy.

 

RE: AC Hi pot Test

(OP)
i forgot to add the reference CENELEC HD 620 S1 part 5 Sction C (indent with the German Norm VDE 0276-620)

RE: AC Hi pot Test

So you are using VLF, should be good. Cant help you with the spec (In the USA) we follow ANSI/NETA, IEC, and IEEE specs, dont have the VDE. Even so, an hour sounds like a long time to test 1 phase.  

RE: AC Hi pot Test

(OP)
While doing this test we are connecting all the three phases of the cable ie L1, L2 & L3 together ,is it right or it should be done seperately for each phase.

RE: AC Hi pot Test

Seperate, you will want to compare the results between the 3 phases, unless you are a testing company that does this for a living and have a large database of test results comparing phases is all you really have to go on for condition assesment.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources