Tension Pile Reinforcing

Tension Pile Reinforcing

Tension Pile Reinforcing

(OP)
Has anyone addressed the issue of a drilled concrete shaft, highly loaded in tension (tower crane leg uplift) and the type of reinforcing laps required under ACI 318?

Specifically, should a 30 inch diameter drilled shaft, loaded to 1200 kips tension be considered a tension tie, thus requiring mechanical couplers rather than lap splices under ACI 318 Section 12.15.6?

Thanks for the help

RE: Tension Pile Reinforcing

I designed some tension piers for a series of large hold downs for a stay-cable supported roof for a stadium project using belled piers with post-tensioning.

I didn't trust the idea of mild steel for a couple of reasons.  One was the required depth of the piers - going down about 80 feet - required a number of lap splices and this made me nervous.  I know that a properly designed lap splice theoretically carries the same tensile capacity of the bar itself.  The issue was that I just felt better with a redundant system in place in addition to the mild steel.

Second reason was in high tension I felt that the piers would be cracked and allow moisture into the section, possibly deteriorating the mild steel over time - even with epoxy coating.

So we used full depth tendons in the piers, prestressed them such that the concrete would not go into tension.

 

RE: Tension Pile Reinforcing

(OP)
Thanks JAE,

Our situation is a little different, we have an intermitently high tension load of a somewhere between a few minutes and an hour duration probably occuring many times a week over the next 3 years.  Corrosion won't be a factor but the presence of a bundled bar lap splice of 100% of the bars, immediately below the pile cap has me concerned.  

I found a paper in ACI Structural Journal Nov/Dec 2005 that says that though it's not permitted under ACI 318, it has been done safely (with some constraints such as staggering the splices, and providing quite a bit of transverse reinf.)

I'm search for someone that has found any other research or has experience with that particular issue of treating a tension pile as a tension tie member.
 

RE: Tension Pile Reinforcing

Hmm, interesting discussion.  We typically don't require anything beyond a lap.  But generally don't have very significant tension piles.  Though I am just finishing a parking garage project, where some piles have fairly significant tension, up to about 40 kips or so.

RE: Tension Pile Reinforcing

just bars that go all the way down.  with laps of course.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources