flux saturation in instrument transformers

flux saturation in instrument transformers

flux saturation in instrument transformers

(OP)
Can a VT experience the same flux saturation as a CT?

RE: flux saturation in instrument transformers

Could, but only if misapplied.  System voltage doesn't vary over nearly the range that currents can.

RE: flux saturation in instrument transformers

metsfan,

When the system is non-effectively earthed, the healthy phases including the VTs connected there are subjected to over voltages during 1Phase-to-Earth Fault. The IEC 60044 over voltage withstand (Rated Voltage Factor)is specified as 1.2-Continuous & 1.9-30sec.

RE: flux saturation in instrument transformers

But if you have a "non-effectively earthed" (ungrounded or high resistance grounded) system then a properly applied VT will be rated line-line and connected line-ground.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources