Load Factors for WS Pipe pressures

Load Factors for WS Pipe pressures

Load Factors for WS Pipe pressures

(OP)
I am designing a 10'deep x 10' x60' concrete trench housing a water supply pipe at a pump station.  The trench need not meet watertightness requirement.  Is the load combination of
(1.4 D + 1.4 F) per ACI 318-08 sufficient for designing the trench walls for lateral thrust from  the pipe pressure? (This is the test pressure specified for the pipe).


   

RE: Load Factors for WS Pipe pressures

I don't know why ACI doesn't seem to respect fluid forces, but I would use 1.7 times your test pressure.  To me it's a live load with the same uncertainties as any other LL.  

RE: Load Factors for WS Pipe pressures

I would assume only the end walls could feel any internal pipe pressure and then only with push joint pipe and rigid connection between the wall of the pipe and the wall of the trench. If mechanical flanges or restrained joints are used, (or a sleeve through the trench concrete), then the walls will never experience the internal pipe pressure.

RE: Load Factors for WS Pipe pressures

(OP)
clampett - I used the conservative 1.7 as you suggested.

civilperson - to clarify, since I may not have explained well the conditions of the pipe.

I was told by the process/mechanical engineer that the wall would be subject to the pipe internal pressure.  
The far end of the pipe in the trench is a dead or capped end, while the joint where the pipe exits the trench is a special flange (referred to on the mechanical drawings as a harness).   I can see where the reaction of the pipe pressure against the capped end should be resisted by the wall unless there was some other anchored element to resist it.  Does this help?  

  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources