Can u give me the formula for calculating Battery room Ventilation ? ...and what kind of material do I use for exhaust ducting to avoid corrosion.
Regards,
Paul
Regards,
Paul
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Battery Room Ventilation
accumulation of hydrogen. The ventilation system shall limit hydrogen accumulation to less than 2% of the
total volume of the battery area. The location should be free of areas that might collect pockets of hydrogen.
Maximum hydrogen evolution rate is 0.127 mL/s per charging ampere per cell at 25 °C and standard
pressure (760 mm Hg).8 The worst-case condition exists when forcing maximum current into a fully charged
battery.
A battery area that meets the above ventilation requirements should not be considered a classified
(hazardous) location;
RE: Battery Room Ventilation
RE: Battery Room Ventilation
Where did you get the info for the maximum hydrogen evolution rate?