Hi,
Anyone can provide me some formula or
computation why a L-G fault is higher that L-L
fault in distribution system mostly with XLPE feeders?
Existing Transformers are solidly ground.
Thanks
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: LG and LL fault
Ik3=VoltL-L/sqrt(3)/X1
Ik1=SQRT(3)*VoltL-L/sqrt((X1+X2+Xo)^2+(3*Rg)^2)
If Rg [grounding resistance]=0 and X1=Xo then Ik1=Ik3.
If the Xo is less than X1 then Ik1>Ik3 - If there is a capacitance connected between live phase to ground –or grounded neutral-for instance[20-30 microF].
Xresult=-L*w/(w^2*L*C-1) L=circuit to ground inductance C= circuit to ground capacitance.
Up to resonance w^2*L*C<1 then Xresult inductive. From resonance Xresult capacitive.
The XLPE cable capacitance is less than PVC as the XLPE permittivity is only 2.3 and of PVC 4-8. For a usual medium voltage cable the parallel resonance occurs only for 400-500 km length.
But, also the transformer winding capacitance to ground may reduce the phase to ground reactance. Usually Xo=>X1 then Ik1=<Ik3.
RE: LG and LL fault
RE: LG and LL fault
RE: LG and LL fault
I3Ø = 3·V/(3·Zs + 3·Zt)
I1Ø = 3·V/(2·Zs + 3·Zt)
I1Ø = I3Ø*(3·Zs + 3·Zt)/(2·Zs + 3·Zt)
RE: LG and LL fault