LG and LL fault

LG and LL fault

LG and LL fault

(OP)

Hi,

Anyone can provide me some formula or
computation why a L-G fault is higher that L-L
fault in distribution system mostly with XLPE feeders?

Existing Transformers are solidly ground.

Thanks

RE: LG and LL fault

Ik3=VoltL-L/sqrt(3)/Z1 Z1=approx.X1
Ik3=VoltL-L/sqrt(3)/X1
Ik1=SQRT(3)*VoltL-L/sqrt((X1+X2+Xo)^2+(3*Rg)^2)
If Rg [grounding resistance]=0 and X1=Xo then Ik1=Ik3.
If the Xo is less than X1 then Ik1>Ik3 - If there is a capacitance connected between live phase to ground –or grounded neutral-for instance[20-30 microF].
Xresult=-L*w/(w^2*L*C-1) L=circuit to ground inductance C= circuit to ground capacitance.
Up to resonance  w^2*L*C<1 then Xresult inductive. From resonance Xresult capacitive.
The XLPE cable capacitance is less than PVC as the XLPE permittivity is only 2.3 and of PVC 4-8. For a usual medium voltage cable the parallel resonance occurs only for 400-500 km length.
But, also the transformer winding capacitance to ground may reduce the phase to ground reactance. Usually Xo=>X1 then Ik1=<Ik3.
 

RE: LG and LL fault

Delta-wye core form transformers can have zero sequence impedance that is lower than the positive sequence impedance.  This will give higher current for L-G fault at the transformer terminals.  

RE: LG and LL fault

I agree with dpc. In core-type transformers Xo = .85 to .9 times X1.In shell type Xo=X1, indeed.

RE: LG and LL fault

Zero-sequence impedance does not include primary system impedance for a DYn transformer.  Pos- and Neg-sequence impedance does.  Assuming primary system impedance Zs1=Zs2=Zs and transformer impedance Zt1=Zt2=Zt0=Zt, then
I3Ø = 3·V/(3·Zs + 3·Zt)
I1Ø = 3·V/(2·Zs + 3·Zt)
I1Ø = I3Ø*(3·Zs + 3·Zt)/(2·Zs + 3·Zt)
 

RE: LG and LL fault

Correct. But Zs<<Zt usually so may be neglected. And in the short circuit case is also an arc resistance, almost always, which reduces the Ik1.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources