Calculating Natural Gas Pressure Drop in a 3" Riser
Calculating Natural Gas Pressure Drop in a 3" Riser
(OP)
Hello,
I need help in calculating pressure drop in a 3" cast iron schedule 40 Natural Gas Riser from cellar to the 19th floor of a high rise building. In the boiler room located on the 19th floor, I will have a Natural Gas Booster Pump that will be sucking gas through this 3" riser.There will be a Caterpillar Natural Gas generator installed on the rooftop which will operate at pressure of 1.5-5 PSI.
Data Available:
-Natural Gas Booster Pump can pump maximum pressure at 2.132 PSI with variable volume from 3000 ICFH to 15000 ICFH.
-Natural Gas Caterpillar Generator required minimum inlet pressure of 1.5 PSI but can operate up to 5 PSI.
-3" riser is approximately 190' tall and will have approximately ten-90 Deg elbows which will add roughly 77' of pipe length to the 190', equaling to 267' in total pipe length.
I need to find out what will be the pressure drop if there is any in this 267' of 3" cast iron pipe. One thing to remember is that the Booster Pump is located on the 19th floor boiler room and not in the cellar floor. I want to make sure that the booster pump can handle all the friction and pressure losses due to the length of this 3" riser.
Thank you very much for helping me with this project!!
I need help in calculating pressure drop in a 3" cast iron schedule 40 Natural Gas Riser from cellar to the 19th floor of a high rise building. In the boiler room located on the 19th floor, I will have a Natural Gas Booster Pump that will be sucking gas through this 3" riser.There will be a Caterpillar Natural Gas generator installed on the rooftop which will operate at pressure of 1.5-5 PSI.
Data Available:
-Natural Gas Booster Pump can pump maximum pressure at 2.132 PSI with variable volume from 3000 ICFH to 15000 ICFH.
-Natural Gas Caterpillar Generator required minimum inlet pressure of 1.5 PSI but can operate up to 5 PSI.
-3" riser is approximately 190' tall and will have approximately ten-90 Deg elbows which will add roughly 77' of pipe length to the 190', equaling to 267' in total pipe length.
I need to find out what will be the pressure drop if there is any in this 267' of 3" cast iron pipe. One thing to remember is that the Booster Pump is located on the 19th floor boiler room and not in the cellar floor. I want to make sure that the booster pump can handle all the friction and pressure losses due to the length of this 3" riser.
Thank you very much for helping me with this project!!





RE: Calculating Natural Gas Pressure Drop in a 3" Riser
I doubt that you're using cast iron pipe. Much more likely that it's steel.
RE: Calculating Natural Gas Pressure Drop in a 3" Riser
I agree that a cast iron riser is much too dangerous for interior building piping. It must be steel.
RE: Calculating Natural Gas Pressure Drop in a 3" Riser
Anyway for a pressure range up to 5 psig and as little elevation difference as 190' i think is safe to assume that elevation does not matter. But if you end up using some fance software and not "hand" calculations then i would included it anyway since most packages handles this "for free".
Best regards
Morten
RE: Calculating Natural Gas Pressure Drop in a 3" Riser
For low pressure gas (which is what I guess you have) the gas pressure will tend to increase with elevation.
This applies to guage pressure only (i.e. the absolute gas pressure in the riser minus atmospheric pressure). And this is what the attachment to vzeos' post states.
Because the gas at low pressure (i.e. approx 2 bar or less) is less dense than air (approx MW 16 v.s 28.97) atmospheric pressure decreases faster with altitude than the internal gas pressure.
The static head loss inside the riser still applies, i.e. subtract rho*g*h from the available pressure at the bottom of the riser.
The absolute gas pressure in the top of the riser will be the pressure available at the bottom minus the static loss minus the frictional loss.
Regards
NMcC
RE: Calculating Natural Gas Pressure Drop in a 3" Riser
Because the gas at low pressure (i.e. approx 2 bar or less)...
In the natural gas distribution industry (at least in the US), low pressure is a specific pressure classification that is usually codified as 4"wc to 12"wc. In other words, low pressure is the pressure delivered to a residence without using a service regulator. Although the op does not specify the suction pressure of his gas booster I suspect it is low pressure because he is using a booster. MMcC's interpretation of gage pressure is correct, however, a pressure of 2 bar (29.00) psig would be considered high pressure in the natural gas distribution industry and reference should be made to the high pressure section of the article I posted.
RE: Calculating Natural Gas Pressure Drop in a 3" Riser
My Natural Gas serive to the high rise building is a low pressure service as VZEOS described. The utility company told me its about 4" WC which is quite low for my generator. My booster pump, pumps out at 2.132 PSI and my generator operates on 1.5-5 PSI. I know this riser will be somewhat pressurized but I want to know what will be the pressure loss due to elevation of 200 feet and would it affect my booster pumps working capacity, as I have only 0.5 psi over the required pressure for the generator. The riser is 3" diameter. Also, all the elbow's and fittings will add to the frictional losses. I assume there will be about 10 elbows. I have been researching this issue for past 2 weeks and did not get a solid answer interms of calculating the pressure drop.
RE: Calculating Natural Gas Pressure Drop in a 3" Riser
The pressure drop calculator recommended by quark in thread124-231787: Pipe or Line sizing software? will probably give you all the accuracy you need.
One thing to note is that with a pressure drop of around 1 psi the gas pressure at the base of the building will be below atmospheric. If the gas riser is supplying the equipment on the 19th floor only then that is not a problem, but if you have take offs lower down you will suck air into the gas system rather supply gas to any appliances. In this case it would be better to locate your booster compressor as close to the utility supply point as possible.
Katmar Software
Engineering & Risk Analysis Software
http://katmarsoftware.com
RE: Calculating Natural Gas Pressure Drop in a 3" Riser
http:/
http://www.pipeflowcalculations.com/
http://w
RE: Calculating Natural Gas Pressure Drop in a 3" Riser
you raise some important issues in booster installation design. Negative suction pressure is always a concern and is never acceptable no matter where you locate the booster. NFPA 54 paragraph 2.11 requires a low pressure shut off device that will prevent the booster from drawing a vacuum on the utility's meter and gas mains. The concern is that a vacuum could cause the meter to collapse and cause pilot flames to be extinguished in the community. The shut off device is typically set to activate between 2 in wc and 3 in wc.
Your calculation is probably good except that sameeji did not supply the load required to properly size the riser. The booster maximum capacity is not the gas load. The gas load is the fuel consumption rate of the Caterpillar gas engine. I looked up the fuel rate of a Caterpillar 450 kW gen set for which the fuel consumption is 4472 scfh, just to do a sample calculation. Using this consumption as the gas load with an equivalent length of 267 ft, a pipe diameter of 3.068 in and an inlet pressure (P1) of 4 in wc, I get an outlet pressure (P2) of 2.255 in wc for a horizontal pipe. If you consider the elevation correction for 190 ft, P2 becomes 3.395 in wc, which would be OK for the given set of parameters.
RE: Calculating Natural Gas Pressure Drop in a 3" Riser
RE: Calculating Natural Gas Pressure Drop in a 3" Riser
ht
RE: Calculating Natural Gas Pressure Drop in a 3" Riser
Will your local NG supplier install an industrial pressure regulator set to the 29th floor NG psi need, thus eliminating the need for installing an expensive and troublesome a booster pump?
At 74th year working on IR-One PhD from UHK - - -
RE: Calculating Natural Gas Pressure Drop in a 3" Riser
You guys are arguing over how many angels can dance on the head of a pin. JUST LOOK AT THE FUEL UTILIZATION CODE FOR THE JURISDICTION, AND/OR CALL THE LOCAL INSPECTION AUTHORITY.
It's just that easy. Really.