What is the applied voltage test for a Hi-Pot testing on the lightning arrestors, CB´s, Disconect switches, etc. in a 115kV substation.

RE: Hi-Pot Testing

Is this an AC or DC HiPot test?  For air break switches and circuit breakers we did an AC HiPot test to twice the rated line to line voltage.  Check the manuals on the CB.  They should have a HiPot value.

------------------------------------------------------------------------
If it is broken, fix it.  If it isn't broken, I'll soon fix that.

RE: Hi-Pot Testing

HVCB is 1.8 times rated.

RE: Hi-Pot Testing

(OP)
Is it for DC power Hi-pot tester? 1.8 times 115KV. Thank you

RE: Hi-Pot Testing

Melco001,
that is the AC value. A test report with the CB should state the HP voltage. The manual should also state the DC, but I will get back to you.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources