System bonding jumper sizing NEC 250.30

System bonding jumper sizing NEC 250.30

System bonding jumper sizing NEC 250.30

(OP)
I have a 1500 KVA (4160 Delta/ 480 Wye) transformer connected to a 3phase-3wire system (no neutral). Grounded at the X0 transformer terminal within the transformer secondary.

Secondary wiring is 6 parallel underground conuits with 3-350kcmils phase conducter per conduit.

My question is how large must the System Bonding Jumper be for each raceway (conduit)?   

RE: System bonding jumper sizing NEC 250.30

Each one must be fully-sized per the table, based on the total cross-sectional area of the phase conductors.  If there is a ground fault in one conduit, virtually 100% of the ground current will flow in the ground wire inside that conduit, so it has to be fully-sized.   

RE: System bonding jumper sizing NEC 250.30

(OP)
Thanks dpc --

The 12.5% calculation for 6 X 350kcmils =~ 300kcmils and to purcahse commerically available wire

I would need 350kcmils bare copper; therfore, each conduit would contain (3) 350kcmils insulated phase conductors and (1) 350kcmils bare copper cable.

Thanks again
 

RE: System bonding jumper sizing NEC 250.30

Sounds about right. It doesn't have to be bare, BTW.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources