Primary duct bank - Utility

Primary duct bank - Utility

Primary duct bank - Utility

(OP)
Is there any possibility of the circulating current due to use of the steel reinforcing bars in concrete encased duct structures (Concrete encased duct banks - 4" Dia. PVC Ducts, 3/4" rebars ) ?

Any assistance will be greately appreciated.

RE: Primary duct bank - Utility

All three phases in each conduit or single phase per conduit?

RE: Primary duct bank - Utility

(OP)
For 500 MCM cable we use only single phase per duct but in case of smaller cable we do run three phase in one duct.
Thanks.
 

RE: Primary duct bank - Utility

If you allow a closed re-bar loop to enclose anything other a whole number of complete three-phase circuits you will have severe heating due to circulating currents.  If re-bar loops see no net current through the loop, then no, you will not have significant heating.

RE: Primary duct bank - Utility

I agree with davidbeach .The ducts- PVC or Steel – will be free of re-bar between but only at the duct bank periphery- around- may be a closed loop of re-bar. A re-bar along the duct-beside the duct- may be provided. In order to hold the ducts only 2-3" concrete will be poured between two adjacent duct without any rebar.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources