I am adding chillers and pumps to an existing variable primary chiller plant. We will have different size chillers and pumps in the common loop. Does anyone have experience with this configuration?





RE: Variable primary chilled water loop
http:
http://w
RE: Variable primary chilled water loop
RE: Variable primary chilled water loop
RE: Variable primary chilled water loop
The bypass line should be sized for the minimum flow rate of the largest chiller. According to chiller producers recommendations, minimum chiller flow should be 50% of the nominal flow. Selecting appropriate bypass control valve deserves special concern. It should have high range ability, stable control of the flow, linear control valves characteristic. Consider using pressure independent control valves.
RE: Variable primary chilled water loop
Accurate system flow control will be the key to your success. A little more information is required:
1.) Are the chillers variable speed?
2.) What is the total tonnage of the chiller plant?
3.) What will be the total number of chillers installed?
4.) What will be the total number of pumps installed?
5.)Are you adding more chillers because the you have added load to your
system or because the chillers were not large enough to begin with?
Controlling dissimilar pumps can be pretty tricky. Parallel pump flow analysis is not a linear relationship and will be hard to accurately predict prior to installation. For instance, if three dissimilar pumps are operating in parallel, three different speed signals may be sent to the three dissimilar pumps for optimum flow control. Some trial and error as far as programming the pump control will probably be required.
My recommendation would be to use a pressure independent 2 way modulating control valve as the bypass control valve. It should be sized for the minimum flow of the largest chiller and should be installed out in the loop such that a chilled water buffer tank is not necessary when a single chiller at low load is operating. This valve should be controlled by differential pressure transducers installed across the evaporators to insure that minimum flow requirements are met.
Lastly, your job will be much easier if pressure independent 2 way modulating control valves are installed at the individual chilled water coils. These valves are like using pressure independent VAV boxes except they are used on the water side. These valves use much less water to cool the space (some even guarantee large chilled water coil Delta T performance). And they can be used as individual flow meters (eliminating the requirement for the large flow meter in the main). Large flow meters in the main do not work very well when the total load is small.
You might try the attached website for some additional help. Good luck.
RE: Variable primary chilled water loop
1) 1 of the 5 chillers will be variable speed
2) 5500 tons
3) 4 chillers
4) 5 pumps
5) we have added load onto the chiller plant
RE: Variable primary chilled water loop
Here are some articles with some other considerations.
http://ww
http:
htt
There are a few more at http://www.kele.com/archive/solutions/ at the bottom of that page, from Gil Avery. He's kind of a guru of variable flow hydronics...
Let us know how it works out for you!
Good on ya,
Goober Dave
RE: Variable primary chilled water loop
FYI
We have just recently worked on a chilled water system that is approximately half the size of the one you are working on and the addition of pressure independent control valves saves approximately $140,000/year (we used $.07/KwH for electricity). This equals about a 2 year payback period. The improvement in control keeps additional chillers from running. The trick is in the programming. Contact me for additional info (jdschmidt@mac.com).
RE: Variable primary chilled water loop
What I noticed is that people put X stand-by chillers, Y stand-by pumps and forget to add a STAND-BY VALVE, which is more likely to fail than a pump. The whole sequence goes out of wack when the valve fails, yet no one ever considers a stand-by valve in teh by-pass.
RE: Variable primary chilled water loop