Relief Valve Sizing for Vessels Containing Solids
The thermal expansion calculations for pressure vessels are based on an empty vessel. If the empty vessel is in a fire and the gas stored starts to expand rapidly the relief valve will protect the vessel from damage.
However, what if the vessel is filled with a solid like desiccant in a heatless dryer. The desiccant pellets will occupy some of the internal space and reduce the volume of gas stored in the vessel.
Is there a correction factor that is applied to the relief valve orifice calculation to allow for the reduction in internal volume?
Thanks in advance for any thoughts.
RE: Relief Valve Sizing for Vessels Containing Solids
Remember the ideal gas law?
Patricia Lougheed
Please see FAQ731-376: Eng-Tips.com Forum Policies: Eng-Tips.com Forum Policies for tips on how to make the best use of the Eng-Tips Forums.
For your first remark, it is very unlikely that a properly rated safety valve ( installed on fired and unfired pressure vessels) would protect a vessel from an external fire because they are not normally rated for a fire scenario.
For your second remark, a properly sized safety valve is rated based on its energy input (BTU/HR, LBM/hr) at a particular set pressure.  It is independent of its volume but having said that it is possible that energy input may be proportional to size (volume) of vessel.