Stud wall overhaning slab edge

Stud wall overhaning slab edge

Stud wall overhaning slab edge

(OP)
I have a perimeter 2x6 stud wall, 1200 plf with the slab edge turned down 9" bearing on a grade beam.  The architect wants 2" of insulation against the slab edge, and wants me to pull the slab edge in 1.5" causing the bottom plate to overhang the slab edge 1.5" so the insulation and wall sheathing are flush which creates the desired clear distance between the brick veneer and insulation/wall sheathing.

I know the grade beam could be widen to get the clear distance, but ignoring the obvious responses is this a typical, detail  are there any pitfalls besides checking bearing and bending of the bottom plate?

Thanks,

RE: Stud wall overhaning slab edge

Termite path through insulation

RE: Stud wall overhaning slab edge

This puts eccentricity in your studs and cross grain bending in your sole plate.   

RE: Stud wall overhaning slab edge

(OP)
Thanks,

I had not considered stud eccentricity.

RE: Stud wall overhaning slab edge

Stud eccentricity would be my only concern, and it shouldn't be much of a problem.  The axial load times the small eccentricity will be a small moment compared to the moment due to wind load.

DaveAtkins

RE: Stud wall overhaning slab edge

If your concerned, bolt an angle to the slab edge to support the bottom plate.

RE: Stud wall overhaning slab edge

Make sure there is plenty of clearance to the ground and that the bottom edge has some supplementary waterproofing.  As noted, it is a termite issue and also an exposure issue for the wood.

Structural issue for a 2x6 is less pronounced than for 2x4 stud wall.  Watch edge distance on anchorage though.  Remember...the guys on the topside drilling anchor holes will shoot for the center of the plate.  If flush with the slab, the edge distance would be about 2-1/2 inches.  As you've been directed to design, the edge distance could be reduced to less than 2 inches.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources