Smoke removal in multi-storey building

Smoke removal in multi-storey building

Smoke removal in multi-storey building

(OP)
What code does it pertain? What is the requirement in term of designing the extract airflow requirement? Does the existing extract fan suitable enough? Is this option only?

RE: Smoke removal in multi-storey building

Is this project in the US? If so, see the 2006 International Building Code. Your specific sections for requirements for smoke control or smoke removal (yes they are different) systems are found in the following sections:

- Atriums over 2 stories in height (IBC Section 404.4)
- Covered malls constructed as atriums over 2 stories in height (IBC Section 402.9)
- Smoke proof exit enclosures in high rise buildings (IBC Section 403.13)
- Underground buildings (IBC Section 402.5)

You have not indicated if this is an active or passive system, although your description causes me to believe it is an active system. In this case, see IBC Section 909 for design criteria.

If you are outside the US and the country has not adopted the IBC, you'll probably apply NFPA 92B, Standard for Smoke Management Systems in Malls, Atria and Large Spaces.

RE: Smoke removal in multi-storey building

(OP)
The project is on the Middle east. I read on the IMC that it is not required if the window is openable otherwise you should design it by 10 ACH.  

RE: Smoke removal in multi-storey building

Seek professional design assistance. You haven't told me enough to make any sort of responsible decision. The 10 ACH value is dated. We don't base smoke control design on ACHs. It's based on the design fire and the smoke movement scenarios.

I can't help you nor can anyone else. Seek a registered Fire Protection Engineer for assistance.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources