Ultrasonic concrete testing
Ultrasonic concrete testing
(OP)
We are currently sounding concrete with a swiss-made ultrasonic instrument call TICO. Literature says that the pulse velocity for indirect or surface transmissio is 5 to 20% lower than the velocity of direct transmission.
In our tests we find the pulse velocity of indirect transmission 50 to 100% lower than the one for direct transmission.
Is anybody out there with experience in ultrasonic concrete testing?
In our tests we find the pulse velocity of indirect transmission 50 to 100% lower than the one for direct transmission.
Is anybody out there with experience in ultrasonic concrete testing?





RE: Ultrasonic concrete testing
RE: Ultrasonic concrete testing
The difference is fairly consistent considering the scatter one has to expect for these readings. Please have a look at attached spread sheet. (I guess we do not have enough readings.) The sounding was done on concrete of different pours. The mix, however is supposed to be the same for each poor.
RE: Ultrasonic concrete testing
Are you following the multiple measurement procedure recommended in the TICO manual? e.g. BS1881 Part 203 NBN B 15.229 as per http://pap
RE: Ultrasonic concrete testing
You are measuring in-situ conditions than can be greater the the "classic" cylinder tests conducted only to measure the properties if the concrete before placement and not recognizing actual placement and curing conditions?
differences in the layer could easily be due to placement/vibration and curing conditions.
I would imagine a greater scatter compared to lab or equipment test results.
RE: Ultrasonic concrete testing
From your link I figure that your are based in Australia. The site we are talking about is an Australian investment in Phnom Penh, Cambodia. The contractor is Leighton. Leighton is struggleing with the concrete quality as the local mixing plants are not yet up to the task yet. Could the phenomenon we are taling about be concrete mix related. I have the impression that the concrete mix is a bit gap-graded consisting mainly of course agreegates and sand.
http:/
http:/
RE: Ultrasonic concrete testing
RE: Ultrasonic concrete testing
Dick
RE: Ultrasonic concrete testing
RE: Ultrasonic concrete testing
The contractor had not only a problem with controlling the mixing plants. Placement, compaction and grout loss were issues, too. This is what kick off the investigation. I'm not supprise that we encounter concrete of different density and strength, even when the cylinders results are good.
My question is more about the difference in pulse velocity between direct transmission and indirect transmission. We learnd from the manuals and books that the ultrasonic signal is much lower for indirect transmission. Therefore the puls velocity is expected to be 5% to 20% lower. On our site the pulse velosity for indirect transmission is only about 60% of the velocity of direct transmission (means 40% lower).
If somebody could tell me that this is possible and can be explained by ... I would be happy.
RE: Ultrasonic concrete testing
RE: Ultrasonic concrete testing
Could shrinkage cracks close to the surface be the cause?
RE: Ultrasonic concrete testing
Significant voiding or porosity can also result in longer path lengths but I'm not certain how much difference it makes between direct and indirect measurements. Usually a lack of signal strength dominates.
RE: Ultrasonic concrete testing
It may be possible that you are not catching the P-wave and the unit detects the R-wave, which is 60% slower than the P-wave.
RE: Ultrasonic concrete testing
Thanks for the replay.
I think overfinishing is not the case as we are talking about walls that were not treated after the formwork was taken off.
If the unit detects only the P-wave and not the R-wave, would this in your opinion be an instrument issue? Or could this also be concrete mix and/or w/c-ratio related?
RE: Ultrasonic concrete testing
You can avoid this problem by using a through transmition configuration.