R.H. couldnt be controlled at fan coil unit as it doesnt contain demumdifier or reheater so i ve reached that any place needs a certain R.H. i must use a n A.H.U. even if the capacity is small because i ve tried to increase the by pass factor to manipulate r.h i even tried to decrease the supply temprature but f course all these tries are not right
RE: controlling R.H.% by hap-4.3
HVAC68