controlling R.H.% by hap-4.3

controlling R.H.% by hap-4.3

controlling R.H.% by hap-4.3

(OP)
hi guys,,

the designing of specified areas at hospitals needs a define value of R.H. like 70% the hap define the resultant r.h. on waht bases and if i want to change the relative hunmidity what shall i do?
thanks in advance  

RE: controlling R.H.% by hap-4.3

It is very difficult to understand your question. Can you split that into multiple sentences? What is hap?

RE: controlling R.H.% by hap-4.3

(OP)
HOURLY ANALYSIS PROGRAMME HAP

RE: controlling R.H.% by hap-4.3

(OP)
the hospital  areas needs to be served by define air circumistances (r.h.%, temp.,ach...etc) how can i make control R.H. value or make it as an input data at hourly analysis prgramme?

RE: controlling R.H.% by hap-4.3

are you talking about the software carrier hap 4.3?

RE: controlling R.H.% by hap-4.3

Under the system tab, for the AHU, click the Dehumdification button. Set the maximum RH setpoint there.

For higher air flows, override the minimum air flow to your ACH in 'Zone Components'

Call a Carrier rep, buy some HAP training... hospitals are tricky.

RE: controlling R.H.% by hap-4.3

(OP)
yes about carrier  software hap-4.3

RE: controlling R.H.% by hap-4.3

RH and temperature control is a balance of space sensible heat gain, space latent gain, supply air temperature, supply air quantity, and supply air humidity.  To use HAP and the effect of the various settings you  need to understand the psychrometrics of the system you are designing before ticking the various option boxes in HAP.  

HAP is very capable software, but no more capable than the person driving it.

One of our grads did a preliminary design for a system with dehumidifation control which basically relied on full cooling with full reheat, technically it would have worked fine, but would have been very energy inefficient.

RE: controlling R.H.% by hap-4.3

(OP)
dear marcoh

R.H. couldnt be controlled at fan coil unit as it doesnt contain demumdifier or reheater so i ve reached that any place needs a certain R.H. i must use a n A.H.U. even if the capacity is small because i ve tried to increase the by pass factor to manipulate r.h i even tried to decrease the supply temprature but f course all these tries are not right  

RE: controlling R.H.% by hap-4.3

Carrier has already introduced HAP version 4.4.

HVAC68

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources