Selecting the correct circuit breaker
I am a trainee control systems engineer and i'm currently designing a panel and i would like to know how to select the correct circuit breaker for my project. I spoke with a colleague in work and was horrified to find out that they guess the correct size and expect me to do the same.
The motor i require a CB for is 3 phase (415VAC), direct on-line and 2kW.
I also require a CB for a 24VDC, 5A PSU.
Some terms that i have seen online whilst trying to research this subject include; "line current", "load current", "FLA", "Inrush current", "power factor" and "efficiency (losses". So if any can clear these up too that would be great!
Any help is greatly appreciated, i'm based in the UK, but feel free to reference to 'NEC' as i've seen in other threads, i believe the uk use 'IEEE' is that correct?
Ross
Ross
RE: Selecting the correct circuit breaker
This is the type of work that should be done by a qualified ELECTRICAL engineer. The fact that you do not know the meanings of the terms you mention indicates that you are not such, and the practice of your co-workers of "guessing" is a fire waiting for a place and time to happen.
Breaker selection needs to be done by first knowing the installation codes of where it is going to be used. Saying that NEC or IEEE is OK for use in the UK is another indicator that you should not be undertaking this task. Please look for and contract with a qualified EE in your area on this.
ScottyUK where are you? This guy needs help!
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
I understand where you are coming from, but i need to learn how to do this regardless.
I am a trainee, so that's why i need help. The company has an electrical engineer contractor that they employ, but he is away for 2 weeks and if i don't find the correct way of selecting a CB they are going to guess the rating and i don't want them to do that.
I am trained in Electronic and Electrical engineering (only to HND level), but the bias was heavily towards electronics, i covered only a small section on transformer efficiency and electrical circuit design.
I know there's alot of talented people on here, hopefully someone can help!
Ross
We have quite a few engineers in the UK who contribute to this forum, so stick around.
BTW, NEC is National Electrical Code - basic installation code in the US. Nothing to do with IEEE.
I looked at the NEC website earlier today and it seems very good, but i can't find anything like it for the uk unfortunately..
I understand that codes could influence things, but surely things like "FLA", "power factor" and "efficiency (losses)" apply to all countries?
To be honest, this is an issue regarding work and i finished nearly 4 hours ago, so i should be getting on with my university coursework, but like i said i'm very keen to find out the answer to this because if noone helps i know i'll be over-ruled and they will just 'guesstimate' a CB rating!
http://forums.mikeholt.com/
http://
I agree with you, it concerns me that i don't know which codes to follow, but i'm very willing to learn and i don't think that my degree course is going to let me know either..
I'm starting to wonder who's responsibility it is to inform students which codes to follow to be honest!
Ross
Load current - current drawn by an impeding load. Can be complex or completely real load.
Line current - Current flowing on a supply line. For example if you're operating three phase, each phase will have its own, possibly different, current flowing.
Inrush current - the current it takes to get an inductive coil energized over the first few milliseconds. Very short in duration but very important for protection. Similar to starting current on a motor (where the starting current is needed to get the motor up to rated speed).
Power factor - Ratio of real power (P, Watts) to active power (S, Volt-Ameres). pf = cos(P/S). S = P + jQ. Q being reactive power in VAr. pf is a complex topic, ask if you need more information.
Believe it or not the power factor looks the most familiar! Is it usually referred to in percentage then? I remember someone saying to me that usually a PF of 0.8 is used, so i assume that's 80% of real power?
Cheers!
Yes, power factor is always less than or equal to one. It is NOT a percentage, though. Do not assume that if pf = 0.8 that it's 80% real power and 20% reactive power (very wrong). Take the sin(phi) and you'll see what I mean. pf = 0.8 yields a reactive factor of 0.6.
Also, you may see "leading" or "lagging" power factor. This is in reference to the current sine wave leading ahead or lagging behind the voltage sine wave.
There's lots of information out there on this. I only began to understand it after a lot of reading.
a) the proper breaker selection has more to do with local fire codes than the specifics of design as you are getting into here, and ...
b) getting it wrong is risking a fire.
Breaker selection is about nothing more than protection against overloading of conductors; both those feeding the equipment and those inside of it (such as motor or transformer windings). Internal equipment conductors will be based on nameplate data on the equipment, so you usually base the feeder conductors off of the same data. So using that, FIRST you select your conductors based on the worst case load scenario your equipment will see, THEN you select the breaker that protects them. The rules for making those selections vary by region / country / state / maybe even city codes.
The reason the NEC says nothing about the UK is that NEC stands for National Electrical Code, with "National" meaning the Nation of the United States of America. It applies absolutely NOWHERE else. It doesn't even apply to Canada, they use the CEC, or Canadian Electric Code. Get the point? You need to find out what the governing installation codes are for the UK. Absolutely nothing else is meaningful to your situation. What is legal and acceptable in Turkey or China or Idontgiveahootstan may be completely illegal in the UK. If you select a protective device based on the wrong codes, it may have an effect on other devices within the facility that are following the code, leaving your installation in a vulnerable position or possibly causing a dangerous condition somewhere else.
whether its human , property, etc. you still have to follow the existing code of your country and locality. since you are in UK i believe you should be using the IEC.
and yes, scottyUK can sure help you.
and remember " a little knowledge is a dangerous thing"!!!
As a general rule you should not be using a CB to protect a motor: normally it is there to protect the cabling and to provide backup short circuit protection. There are breakers designed for motor duty but they are less common. Your motor should have a proper thermal overload relay to protect it, and again without knowing anything about the load it could be a Class 10, 15, 20 or 30 O/L relay. Class 10 is most common over here but it depends on the requirements of the load. You should have a contactor switching the motor, which I hope you have.
BS 7671 is the UK wiring regulations for fixed installations. The standard which is most relevant to your task is probably BS EN 60947. If you want an easier read than the BS then (e.g.) the Siemens and Telemecanique catalogues both have a lot of useful selection guides which will probably help you. They're much easier going than the standard, but the standard is what you need to comply with.
Have a look at the modular motor starters available from the bigger manufacturers, which give you a breaker, contactor and overload in a type-tested combination. They are getting quite common for small loads and can give you an easy design solution if your load and motor is close to what the manufacturer used as their 'typical' parameters.
Please get someone to check your design before it gets built.
I'm sure about the source of the 415VAC 3phase supply to the motor. All my panel will do is switch it on and off using a digital output on a siemens PLC (via a contactor).
The CB is there for the installers to wire in/out to and all the information i have on the motor i've stated (Direct On-line, 2kW, 415VAC 3Phase).
ScottyUK: The standards that you are referring to, are they available to free download? Are we in the UK obligated by law to abide by the standards?
Do the standards contain all definitive information on selecting CBs, cable size, etc, etc.
I've struggled with things that people who design panels must think of simple tasks, such as how to layout the control panel. I can't find any books or information on this area, but it must be documented somewhere.
Thank you for your time people.
Ross
I'm slightly alarmed that the company you work for would just 'guess' at a suitable breaker size to protect a circuit. No-one but a trained Electrical Engineer should be doing this. By asking you to do this without training they are asking you to break the law as I see it - if there was a fire as a result of an incorrect breaker being fitted and somebody died, we are talking corporate manslaughter here.
It's fine if you are training, and you are being asked to do this so that you can learn, so long as somebody competant is checking your work before any installations take place.
That aside, there is more info required here. Firstly, the panel you are feeding the motor from - what type is it, MCCB panelboard? MCB Dist Board? Fuse board? MCC Panel? Then there's the cable supply to the motor - the breaker you install must be suffiently rated to not only not trip when the motor starts, but to trip in time to protect the cable and prevent overload on the circuit.
Then there are many other considerations - what capacity do you have on your electrical system to add extra circuits? Will the breaker you install achieve discrimination with any upstream devices? Is it suitably rated for the fault level that it is likely to encounter?
In very simple terms, a 2kW motor at 415V (if it really is 415V and not 400V as it should be in the UK, although it makes little difference at this low a load) will draw about 5A running current, although the starting current could be much higher, and your breaker will have to be suitably sized to clear the starting current, or else suitably in-sensitive so as not to trip as soon as an overload is detected.
I have to admit i was told that the supply was 415VAC by someone else, i've not been able to confirm it myself (yet).
The panel is a control panel containing a Siemens PLC and whatever additional parts are required for controlling the motor(s). As far as i can see it will connect like so:
3 Phase wired into CB > Contactor (PLC Digital output controlled) > Motor
Does that seem correct? The panel is also receiving 4-20mA signals from various pressure transmitters and temperature sensors which as also fed to the PLC and viewed via a HMI. There are 2 motors being controlled (2KW) and 2 Pumps (1 lobe and 1 hot water supply; 2KW and 3KW respectively).
I've recently found out that i need to design an emergency stop circuit for the panel, i wont bring that into this topic properly because unfortunately i've discovered that it's also a complicated subject (sigh).
I've identified the standards required for the E-Stop ciruit and others have stated the standards regarding circuit breakers, but how do i get access to them? Is it free of charge? Does every uk business have to abide by them because i just don't think my company (it's a small one) even uses them, but i really want to make sure i do if it's required by law.
Thanks again people.
The compliance with relevant standards depends on the locale, and the particular standard being referenced, but I'd say its safe to say that for most electrical applications, the referenced standard is law.
Designers, installers and so on thus have an obligation to ensure that whatever they design, commission, install and so on complies with the relevant standard, and thus the onus is on them to provide the relevant standard. I do not believe it is possible to state that something is designed to a standard without having the ability to refer to the standard when required.
If your employer doesn't have access to the standards, or worse, refuses to provide them, then unfortunately its probably better for you if you look elsewhere. Observing mistakes can sometimes be a great way to learn, but in these applications to embark on such a process is at best foolhardy, and at worse likely that you'll end up in court. Rest assured that any company that feels that it can avoid its duty to design to an appropriate standard is not likely to think twice about providing a scapegoat when (not if) the proverbial excrement hits the air propulsion device.
I've only just joined the company and it's a very small one, they currently contract thier electrical work to a self employed electrical engineer and they've not once mentioned standards. I can't imagine the bosses reaction when i say "can you please buy me this £300 standard?", especially if there are multple standards to purchase (which there obviously are). If i'm going to ask such a question i definately want to know whether said standard is required to be complied to by law or otherwise i'll just get a straight "NO" as an answer to my request.
Prior to this company i did an apprenticeship at General Electric and i definately remembered the engineers there mentioning standards and directives.
Thank you all for your replies.
You can buy the regs from anywhere such as WH Smith or from Amazon (regs + on site guide, which would be useful for someone like yourself, about £70)
I just called the British standards enquiries line to ask them about that area. They said that british standards are a guide, but when following a regulation they are required by law.
So my new task is identifying regulations to follow. So as you said there are the wiring regulations (BS7671:2008), but how would i find out any other regulations to be followed? Also, within the BS7671:2008 regulations, will they reference to other british standards that must be followed (therefore making them compulsary by law)?
I'm starting to think that a) I should get the company to buy a copy of BS7671:2008 and b) Is it compulsary to have completed the City and guilds 17th edition to design electrical installations.
Any ideas, people i can call, etc?
Ross
As I noted previously the BS 7671 wiring regs apply to installations, not to equipment. The most relevant standard for equipment is BS EN 60947. Part P is irrelevant for a non-domestic installation.
cha1n,
In answer to your question, it is not technically a legal requirement to conform to the relevant Briitsh Standards, but by doing so you 'usually' do meet your legal obligations although it is not implicit in the standard. If you decide to ignore the standards and it goes wrong then the prosecution's case will probably focus on why you, as a competent person, believed that you knew better than the authors of the standard when you designed whatever it was that caused the incident. It's a pretty much indefensible position - much easier to comply with the standards!
Have a look at http://www.schneider-electric.co.uk
You'll have to register to be able to download some information, but search for 'DIA1ED2061002EN' in the search field. This document gives some information which I think might help you understand the subject a little more and which contains some equipment combinations which will be suitable for 'typical' applications near the back.
Firstly, thanks for the reply. You mention that BS EN 60947 is the most relevant standard for equipment. If in future i wanted to find the correct standard to follow for my particular application, how can i find out?
I was about to order a copy of BS 7671 and i assumed that as it was the regulations for wiring that it would contain details on sizing CBs etc, but it seems like you're suggesting that CB sizing guidelines are found in a seperate BS, do i understand correctly?
BS EN 60947 is titled Low Voltage Switchgear and Controlgear. It's a big standard with a lot of parts (i.e. it is f'ing expensive) and like most of the British Standards, including BS 7671, it tells you what you must achieve but not how to achieve it. The engineer's job is ensuring that his design meets the standard, and part of that is being able to interpret the standard and apply it to the real world. The manufacturers have a vested interest in selling equipment which either complies with, or is easy to design into a system which complies with, a standard. That's why I suggested the Schneider website as a starting point. Siemens have some good guide material on their site too, as do others.
The cheapest way of finding standards is time spent looking on BSI's website or occasionally the IEC equivalent using the search engine. There's a standard for almost everything if you look hard enough. Some are pretty obscure to say the least.
I feel i'm digressing from the topic, but another issue i've just encountered is wire colours. Does the wiring regs state correct wire colour for all voltages?
I'm trying to find out if there are set cable colours for 24VDC wiring and for field and local wiring to PLC I/O Cards.
Cheers,
Ross
Is the design work to be done by a professional engineer?
Is there an equivalent in the UK to UL508A - which is a panel shop listing. We are a registered UL508A panel shop which allows us to build industrial control panels and apply a UL label. This has a UL standard and random UL inspections to ensure we are meeting the standard.
Yes, I would expect it to be designed by a professional engineer. No, there's not a direct equivalent to UL508A as far as I'm aware, although there probably should be. My impression is that (some of) the US standards are more practically oriented than the European equivalents. Some of our standards are written by lawyers for lawyers, or that's how it feels.