(OP)
What loading should swimming pools be given behind MSE walls?  There seems to be differing opinions out there.  Assuming the pool load is within twice the height of the wall.

RE: Swimming pool load

Above ground or below ground pool?

RE: Swimming pool load

Horizontal load of 62.4 pounds/sq. ft. per vertical foot.

RE: Swimming pool load

(OP)
Sorry BIG H, it will be below ground gunnite with a paver deck around the pool.  New information says it may be 6 feet away from a 8 foot height section so it will be in the zone of influence.  

I thought a dead load of 150 to 250 psf might be in the range but just do not have the experience as a non engineer to know that to be true.

Thanks for the help on this one.

RE: Swimming pool load

- had this written once before but unreliable connections out here.

Your MSE wall would be reinforced for about 0.7 to 0.8 times the height of the wall - i.e., 5.6 to 6.4 ft (see BS8006).  Therefore, the pool would not be within the zone of the reinforced mass and therefore not within the zone of influence of the active earth pressure 'failure plane'.  (45 + >30/2 or >=60 from horizontal.  The horizontal pressure that civilperson indicated would be an "overturning" pressure against the reinforced mass - but as you don't have soil - only water, for this height of wall, it is basically (not quite true) a wash.  Check the global stability of a slip surface going from behind to underneath the wall - if okay, I'd say you would be okay.  Of course, your "wall" must satisfy sliding and overturning which, for the mass described above, I see no reason it wouldn't.

RE: Swimming pool load

(OP)
BigH, thanks again, I know we have done a number of walls in front of pools but have never had a firm confirmation on the nature of the load.  We have always left it to the wall designer to work it out.  Now I have a designer wondering which is the right way.  I will look into getting a standard for us on this.  Our water issue we have also suggested all gravel backfill and drainage through the wall in case of leaks.  In cases of pools on slopes we have suggested global stablity be run especially with life issues and larger pool deck areas.  

RE: Swimming pool load

When the pool splashes over the edge of the pool and saturates the backfill of the MSE wall to the depth of the pool, a horizontal force will exist.

RE: Swimming pool load

only if 'enough' water splashes over the edge to saturate the fill.  In any event, the reinforced zone fill, being granular, would drain the water faster (downward) than the water actually mounding up within the fill I would think. And also, water would seep out between the facing panels if it does want to "rise".  As a worst case - use a "near surface" hydrostatic force and I think that you would find for a 8 ft wall, it will make little difference in practice.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources