CURRENT TRANSFORMER

CURRENT TRANSFORMER

CURRENT TRANSFORMER

(OP)
What  parmaters  must  be  checked  during  the  process  and Final  Testing QA  of  Current Transformer upto  132 KV ?
What  is  the basic  difference  between the Measuring and  
Protective CT &  PT ?

RE: CURRENT TRANSFORMER

Please refer a thread under subject Switchgear/boards/relays/motors engineering

RE: CURRENT TRANSFORMER

ANSI-rated instrument transformers have two general classes—metering- and relay-class.

Relay class devices can generally be successfully used for metering, but the reverse can be a serious mistake.

Reference IEEE C57.13 and C12.11
  

RE: CURRENT TRANSFORMER

For VTs, metering (measureing) and protection (relay) designs are essentially the same. In the US, most wound-type VTs come with a metering accuracy rating, which can be used for relaying purposes (overkill).

CTs are a different story. Metering accuracy CTs are designed to be accurate at currents present during steady-state conditions (i.e. nominal current +/-?%). Relay rated CTs are designed to maintain some accuracy during system faults. In the ANSI market, they are designed to be +/-10% accurate up to 20 times rated current and are rated in terms of the voltage that can be developed across the secondary winding.

In the IEC world, there are many ways to rate relay class CTs. 10P20 at some VA is the close equivalent to the ANSI C class. C800 would be close to the IEC 10P20 - 200 VA, assuming a 5A rated secondary. Most IEC installs use 1A secondary and the math gets a little more confusing.

It is true that most relay rated cores have a metering accuracy at nominal current, however, the factory test procedure for testing relay and metering cores is quite different and normally the routine test reports will not give enough information about the relay rated cores to assume a suitable metering accuracy.

Hope this helps.

RE: CURRENT TRANSFORMER

Sorry...forgot to address your QA question. Since you mention 132 kV, I assume you're in the IEC world. From an insulation standpoint, IEC requires/recommends a hi-pot test on primary and each secondary to ground, partial discharge test (done with hi-pot test), insulation capacitance measurment (before and after hi-pot) and dissipation factor (insualtion power factor). Of course an accuracy test is also required and this varies with how the unit is rated. The applicable standard is IEC 44-1 (was IEC 286).

The partial-discharge criteria varies with insulation type, i.e. oil-filled vs. dry-type.

RE: CURRENT TRANSFORMER

what is the basic defination of CT and PT in power stations.

RE: CURRENT TRANSFORMER

CT = current transformer
VT = voltage transformer

They step either current or voltage from the line level to some level that meters and relays are able to handle. In the US, normally the secondary voltage of VTs is 69/115V and the secondary current rating of CTs is 5A.

Their main performance parameter is how accurately they make the transformation.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources