Laundry equipment heat gains
Laundry equipment heat gains
(OP)
How can I calculate the heat gains (airconditioning load) of the laundry equipment? KW = steam rate X enthalpy x factor? Where can I get equipment factor?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Laundry equipment heat gains
|
RE: Laundry equipment heat gains
If its of any scale, its an air handler exercise.
If its a Local Coin Op: Triple the normal for the Sq Ft of space, like it was a retail store....And take controll of the drier intakes.
And the chemistry can be fun even then...
Most of the heat input goes down the drain with the wash water...Most of the AC load comes from the water steaming off the clothes or ?? when they are removed from the machines. The heat losses from the machine enclosures are substantial but fairly simple to identify...The surface temps can't go past 115 at 90 ambient so unless there is forced air circulation from them you will only encounter about a 70 to 90 BTU/Sq. Ft. of SM heat loss...
The much larger topic: How many CFM to the Driers and in what form are you going to supply it if you are going to keep the surroundings cool?