Reference as per Canadian Code for total deflection L/240
I need code reference for dead + live load deflection to be not greater than L/240 as per Canadian Code.
For concrete it is Table 9.3 CSA A23.3-04, under 9.8.5.3
but looking as per steel for floor area in question.
RE: Reference as per Canadian Code for total deflection L/240
Is it showing dead plus live shall not be more than 240.
Dont know if you need something specific to steel.
Ultimately, most deflection limits are actually just recommedations anyway, so you will not find a "code based limit" per se.
If you read clause 6.3.1.1 of the steel book, it says "see Appendix D for recommended values for deflection".
Actually that number is important from a point of view if you have finishes above floor, it prevent it due to excessive deflections. That number might be our company derived, but i need specifically for concrete deck on steel beams/joists.