Masonry infill wall in RC moment fame.
How you guys model masonry infill wall in ETABS? ASCE 41 suggests using equvalent compressive strut to consider the effect of infill walls. Is there anyone who had done this before? Any comments will be thankful.
RE: Masonry infill wall in RC moment fame.
http://www.buscalibros.cl/libro.php?libro=614772
There must be an english edition, I think.
In fact towards 1980 I designed a table to design and stabilize (small) fully isostatic steel structures with infills this way. I am sorry not to give the exact detail because the book is behind such amount of things I can't reach it without spending half an hour or more in the task.
It basically gives the strut geometrical configuration and the recommended checks.
You may also take a fundamentals approach: divide the inclined load in shear and a normal on the layers of brick. What effective section to take the forces, one can assume conservative values.
Also, the CBPI_manual4
D e s i g n o f C l a y M a s o n r y
f o r W i n d a n d E a r t h q u a k e
of Clay Brick and Paver Institute has a section for in plane loads for panels of brick. I have searched the web a bit and seems removed (whereas companion manuals are not) hence I assume it is seen outdated from the current codes' viewpoint. I have got a pdf copy of it and if you want I may send it to you.
h
I have also seen, and there must be tutorials for designing masonry buildings in ETABs. Look for them in the web.
http://db.nzsee.org.nz/2001/papers/40201paper.pdf
Yeah, I have it 3 meters from me. Section 7.4.2 in the book, 8 pages long, hence better ferer you to the artible.
Seismic Design of Reinforced Concrete and Masonry Buildings
T. Paulay
M.J.N. Priestley
Wiley Interscience NY 1992
Design of Infilled Frames
p. 587 to 595
For the masonry compression strut forming between opposed nodes of the diagonal it gives an effective width of 0.25L where L would be the length of such diagonal, but then the checks follow and are not so easily transmissible.