Who knows something about "recurrent surge osciloscope measurement method" will be done on the rotor of synch. generator?. Would you like to share your knowledge with me?
thanks.
zub.
thanks.
zub.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: rotor testing
To apply this test to the rotor of a synchronous machine, you must (assuming series connection) find the center point of the rotor circuit and compare each half of the winding. This test is similar to a voltage drop test in that it will determine if there are any shorted coils.
RE: rotor testing
But beware. It may be considered a destructive test if the windings are already weak or if the test is not done properly. Selection of voltage is important... too high can fail a good winding.... too low may not detect a marginal winding.
Try searching for Baker motor surge tester.
RE: rotor testing
http://www.irscoil.com/qualitycontrol.shtml
http://www.joliet-equipment.com/rebuilding_process.htm
(indicates when it is done during the rebuilding process)
Also, see
Nailen, Richard L., "Understanding Surge Comparison Testing," Electrical Apparatus, Vol 48, No 12, December 1995, pp 27-31
The above testing is for variation to diagnose an insulation condition. Also, it reveals improper winding connections, unrelated to dielectric integrity.