All,

We have 4160V switchgear L-L, a 3W setup with ground (no neutral bus).  

We have to input voltage for relay operation of overvoltage, undervoltage, as well as other relay settings we're picking up on.  My question involves suggested connection of potential transformers.  We usually use single phase transformers for each phase, with a fuse on both the primary and secondary sides of this transformer.  

For a 480V system, I haven't physically seen how it's wired but I've always assumed that we go line to neutral on the primary side, and that's where our 2.3 turns ratio comes from...  277/120 ~ 2.3 ...   But for a 3W system us younger engineers were questioning both physically where you would connect the primary of the PTs to, and what turns ratio you would use.

Thanks in advance for shedding light on this.
 

RE: Potential Transformer in 3W Switchgear

Typically on a 3W system, you would connect 2 VTs open delta, 35:1 (4200V/120V), with secondary B phase grounded.
 

RE: Potential Transformer in 3W Switchgear

Traditionally it would be two PTs connected open delta - 4200 V - 120 V  (35:1).

 

RE: Potential Transformer in 3W Switchgear

(OP)
Can you guys further explain the open delta?

Are there other options you can use?

RE: Potential Transformer in 3W Switchgear

Hi.
Please see attached thread.
In end of thread you can find pict of few types of connections.
thread238-216248: Open Delta PT vs Wye PT
Good Luck.
Slava.
Jghrist and Dave, next time, could you please coordinate your posts, same grading smile  

RE: Potential Transformer in 3W Switchgear

Read the thread referenced by slavag.  I certainly wouldn't recommend open delta VTs.  Sure you can save a buck, but when you need to really figure out what happened you will find that some of the necessary information was never recorded when using open delta, and that information can never be recovered.

RE: Potential Transformer in 3W Switchgear

On an ungrounded delta system, I'd be somewhat cautious about using wye-wye PT connection due to the potential for ferroresonance.  

 

RE: Potential Transformer in 3W Switchgear

Quote:

3W setup with ground
Probably won't have to worry about ferroresonance.

RE: Potential Transformer in 3W Switchgear

Yup, missed that little tidbit.  For some reason I had a delta system in mind.

Three wye-wye PTs would be OK.  You could still use the 35:1 PTs and would have 69 volts line-neutral and 120 V phase-to-phase.  

 

RE: Potential Transformer in 3W Switchgear

Or use 20:1 (2400:120) and have 120V line-neutral and 208V line-line.  Any other ratio that floats your boat but keeps the secondary voltage low enough for your equipment should be fine.

RE: Potential Transformer in 3W Switchgear

(OP)
I hope you guys get paid handily for all of your knowledge.  One day hopefully I'll be there...  So the natural follow up involves, what is ferrorresonance and why does it apply (I assume) to a 4W but not a 3W system?

Thanks for the resources

RE: Potential Transformer in 3W Switchgear

It can occur when wye PTs are connected to an otherwise ungrounded (delta) system.  The inductance of the PTs resonates with the capacitance to ground of the system and creates very high voltages, and sometimes PT failures.  

If your system is grounded at the source, this shouldn't be an issue.   

RE: Potential Transformer in 3W Switchgear


I am confused as to why the B phase on the secondary of an open delta PT is grounded.  I would think that you would just connect the B phase or corner of the delta directly to the B phase input on whatever meter is being used.  I cant seem to see exactly why this is grounded.

So if you are reading Vab on the secondary I'm assuiming this should be a L-L measurement but it seems like it would be a L-G measurement with B grounded.

RE: Potential Transformer in 3W Switchgear

Hi Rockman7892.
Please draw for you voltages vectors and you will understand, why you confused.
If you maes Vab 120V w/o grounding of B, you will meas same voltage with grounding.
If you have wye connection ( star connection) you can connect grounding to star point or to B phase, but L-L and L-N voltage will be same with or w/o grounding point.
Grounding is safety and reference issue only.
Hope that helps.
Best Regards.
Slava
 

RE: Potential Transformer in 3W Switchgear

Slavag

I see it now.  Thank You.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources