Ground Fault Currents in delta connected circuits

Ground Fault Currents in delta connected circuits

Ground Fault Currents in delta connected circuits

(OP)
Hi all,
how would be the distribution of positive, negative and zero sequence currents for a single line to ground fault in a delta connected circuit at say 35kV?
would the zero sequence dominate or otherwise?
The upstream circuit has a delta-star(high impedance grounded) transformer feeding this faulted delta on the LV bus. The ground fault current will return to the high impedance grounding connection in the transformer LV.
thanks!
 

RE: Ground Fault Currents in delta connected circuits

Hi Zing22.
Ground fault in the isolated system ( that menat delta connection w/o any grounding trafo)=0.
Actually is equl to capacitance current of all elements.
Upstream system maybe fill some unbalance.
Regards.
Slava

RE: Ground Fault Currents in delta connected circuits

If you have a resitance grounded wye winding supplying this system, then you don't have a delta circuit.  You may have delta connected loads, but that is not a factor.  

If you have ground fault, the current will have to get back to the transformer neutral point, via whatever path it can find and then through the resistor.

It is a straightforward line-to-ground fault in terms of symmetrical component analysis, except that you must include the grounding resistance in the zero sequence impedance or the fault impedance.  

But maybe I'm not understanding what you are trying to ask.

  

RE: Ground Fault Currents in delta connected circuits

I1=I2=I0

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources