Plastic Tank in a Classified Area
Plastic Tank in a Classified Area
(OP)
Hello,
We have a silicone storage tank in a Class 1 Div 2 area. Even though silicone is not flammable, there might be a slight concern that flammablew vapors could get into the tank and a spark from transferring silicone could cause an issue. Here goes some other things pertaining to this:
- silicone is a conductive fluid
- silicone transfer rate into the vessel is very low (around 1 ft/sec)
- silicone gets transferred there only once a week
- there is no dip tube in the tank
- tank is atmospheric
From past experience, any thoughts on issues with not having the tank bonded or grounded because its plastic? I don't think so because of the slow transfer rate and conductivity of silicone (even though there is no ground for the charge buildup to go to).
Thanks.
We have a silicone storage tank in a Class 1 Div 2 area. Even though silicone is not flammable, there might be a slight concern that flammablew vapors could get into the tank and a spark from transferring silicone could cause an issue. Here goes some other things pertaining to this:
- silicone is a conductive fluid
- silicone transfer rate into the vessel is very low (around 1 ft/sec)
- silicone gets transferred there only once a week
- there is no dip tube in the tank
- tank is atmospheric
From past experience, any thoughts on issues with not having the tank bonded or grounded because its plastic? I don't think so because of the slow transfer rate and conductivity of silicone (even though there is no ground for the charge buildup to go to).
Thanks.





RE: Plastic Tank in a Classified Area
RE: Plastic Tank in a Classified Area
RE: Plastic Tank in a Classified Area
<<A good friend will bail you out of jail, but a true friend
will be sitting beside you saying " Damn that was fun!" - Unknown>>
RE: Plastic Tank in a Classified Area
Thermally conductive, yes, but many silicones are not electrically conductive and are in fact used as insulators.
Generation of charge during transfer would depend on a number of factors. If you think you're going to get a charge build up then you need to have some way of dissapating that safely.
If your stainless steel tube is properly bonded then you may only need to consider flow into/through/out of the tank.
RE: Plastic Tank in a Classified Area
RE: Plastic Tank in a Classified Area
Review NFPA-30....it contains requirements for metallic tanks in both flammable and non-flammable service.
Also compare the cost of the plastic tank versus a production grade thin-walled 304SS tank....probably not much difference.
-MJC
RE: Plastic Tank in a Classified Area