2300V Motor Cable per NEC 310.6
2300V Motor Cable per NEC 310.6
(OP)
I am having difficulty interpreting the NEC 310.6 Article. One of my co-workers told me that only 4160V motors are required to have shielded cables to the motor. He explains that the 2000V and above is a line to ground rating and that 2300V motors would fall in the under 2000V case since its L-N rating is 1328V. Is this correct? I believe it is but want to get others to throw in their 2 cents. Thanks in advance. I have listed two references that support's my co workers case but both articles do not mention 2300V motors. Are there any other good references?
References
ht tp://ecmwe b.com/nec/ electric_b ehind_nec_ changes_3/
ht tp://searc h2.southwi re.com/sea rch?q=cach e:w9tQ9YWi qggJ:www.s outhwire.c om/process GetArticle .do%3Fcomm onId%3D0d8 df24ceca6a 010VgnVCM1 000002702a 8c0____+ne c+310.6+(s ite%3Awww. southwire. com+)& access=p&a mp;output= xml_no_dtd &ie=UT F-8&cl ient=south wire_front end&si te=southwi re_collect ion&pr oxystylesh eet=southw ire_fronte nd&oe= ISO-8859-1
References
ht
ht





RE: 2300V Motor Cable per NEC 310.6
"Approximately half of all "5 kV" circuits actually operate at a voltage of 4,160 volts.
These and similar circuits will now have to be wired with shielded rather than nonshielded cables. Most of the remaining "5 kV" circuits actually operate at 2,300 volts or similar voltages. These lower voltage circuits can continue to be wired with non-shielded cables as long as the cables are Listed as Type MV-90 or MV-105 cables by a qualified testing laboratory ".
See :
http
That means new 2005 NEC is referring to L-L voltage and not to L-N voltage.
Regards