We have several Squirel cage induction motors running on our plant at well below their power rating   e.g. 345kW 3.3kV four pole 50Hz motor full load current 75 amps. with a power factor of 0.8 at full rated power. I understand that if you run a motor at well below its rated capacity
(in this case absorbed power 146 kW ) The power factor drops markedly . can anyone help with the formulae and calculations to work out the power factor at duty point and the magnetising current.

RE: Induction motor magnetising current and power factor at duty point

Use the equivalent circuit of the motor. You'll find the circuit in books on power system analysis. The circuit and a program for the parameters can also be found at http://pp.kpnet.fi/ijl/prog.htm

Alternatively, use a computer program for power system analysis to calculate the current etc, for example at http://pp.kpnet.fi/ijl
 

RE: Induction motor magnetising current and power factor at duty point

Simply put, the magnetizing current is constant when voltage is constant.

It can be calculated as In*sqrt((1-cos(phi)^2). In your example the magnetizing current is 75*sqrt(1-.8^2) = 75*.6 = 45 A while the torque producing current is 75*.8 = 60 A.

This current stays roughly constant when shaft load changes so, at 146 kW, your torque producing current will be 60*146/345 = 25.4 A. Your total current will then be around 65 A and the PF is 25.4/65 or around .4 not so good.

This is a rough calculation, but the result should not be too far off the actual value.

 

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources