Power Panel Loading Calculation

Power Panel Loading Calculation

Power Panel Loading Calculation

(OP)
I have the following 120V-3Ph-Delta panel that contains the following phase loading:
AB: 5.3A
CA: 13.0A
BC: 11.2A

How do I calculate the feeder ampacity? The drawing that I have shows a 21.0A load. Not certain how this number was calculated.

RE: Power Panel Loading Calculation

Can you post the drawing?  Your terms are a little confusing, I'm not familiar with currents called out with two letters...

Good on ya,

Goober Dave

RE: Power Panel Loading Calculation

For feeder calculation, I would assume equal loading on all three phases at the highest load. That would be 1.73 x 13 = 22.5 amps.
It looks as if the original designer vectorily added 11.2 and 13. That would be close to 21 amps.
AB, BC, CA means that the loads are connected line to line from "A" phase to "B" phase, from "B" phase to "C" phase and from "C" phase to "A" phase.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Power Panel Loading Calculation

Ah, thanks Waross.  I missed the part where everything is 2-pole...  I'm not used to 120V delta.

If the load were perfectly balanced, it would be a matter of summing the currents and dividing by 1.732.  In your case, 29.5/1.732 = 17.0 amps, times 1.25 to size the feeder = 21.3.

However, with such a small number of 2-pole circuits, balance is hard to come by, so Waross's suggestion of assuming balance at the highest expected load is best.  You should throw in some extra capacity for the spare breakers too.

Make sense?

Good on ya,

Goober Dave



 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources