Basement parking area ventilation

Basement parking area ventilation

Basement parking area ventilation

(OP)
We have three basement carpark level in my building and ventilation is very poor. I am planning to put a exhaust system in order to have an air circulation in the Basement. I just want to know guys what can you suggest to me the airflow rate for the basement parking area and what type of exhaust fan that suites for exhaust system in the basement parking area. Thanks

RE: Basement parking area ventilation

As per IMC, 1.5 CFM/SQ.FT. for parking garages.

RE: Basement parking area ventilation

(OP)
What is IMC?

RE: Basement parking area ventilation

International Mechanical Code

RE: Basement parking area ventilation

(OP)
Many thanks....

RE: Basement parking area ventilation

We typically control these ventillation systems with Carbon Monoxide (CO) sensors, approximately one sensor for every 5,000 to 7,000 sq. ft. and activated to operate the ventilation system when the CO reaches 25 ppm, this helps save energy in multiple ways by not having the ventilation system running when the air quality is OK, not contaiminated by vehicle exhaust (CO).
Make-up air requires heating in the winter, cooling in the summer, as well as the enormous amount of power ventilation systems of this size draw.

Ron S.

RE: Basement parking area ventilation

Canadian Building Code requires 0.75 cfm/sq.ft... wonder why the IMC is so much higher?

We typically provide this airflow controlled by CO/NOx sensors as outlined by 'gasdetector' above.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources