I've been doing web searches for quite some time trying to find a solenoid valve capable of sealing off liquid flow even if a large differential pressure exists between the outlet and the inlet or vice versa. In other words, the valve should remain tightly closed in both of the following situations:
1) 100 psig on the inlet, 0 psig on the outlet
2) 0 psig on the inlet, 100 psig on the outlet
Most solenoid valves I'm aware of will open if outlet pressure greatly exceeds inlet pressure.
Furthermore, I need a valve with a Cv of 1.5 or greater to keep my pressure drop in a reasonable range. I have yet to find a valve that meets all these criteria (on, and material compatibility with DI water and glycerin). I've used keywords like "bi-directional" but I'm not sure if that's what I want or not.
What is the common name for a valve with these characteristics? Who supplies them?
Many thanks.
Juston
1) 100 psig on the inlet, 0 psig on the outlet
2) 0 psig on the inlet, 100 psig on the outlet
Most solenoid valves I'm aware of will open if outlet pressure greatly exceeds inlet pressure.
Furthermore, I need a valve with a Cv of 1.5 or greater to keep my pressure drop in a reasonable range. I have yet to find a valve that meets all these criteria (on, and material compatibility with DI water and glycerin). I've used keywords like "bi-directional" but I'm not sure if that's what I want or not.
What is the common name for a valve with these characteristics? Who supplies them?
Many thanks.
Juston





RE: Need a valve that can handle pressure on the outlet . . .
htt
Ted
RE: Need a valve that can handle pressure on the outlet . . .
RE: Need a valve that can handle pressure on the outlet . . .
Joe Lambert
http://www.control-associates.com/
RE: Need a valve that can handle pressure on the outlet . . .
Let us know what you decide to do!
Good on ya,
Goober Dave
RE: Need a valve that can handle pressure on the outlet . . .
You might look at Maxon for solenoid valves with more horse-power. Unless there is something special, I would go with the actuated ball valve.
RE: Need a valve that can handle pressure on the outlet . . .
Thanks for the tips. This is an avenue a colleague of mine also suggested I pursue.
RE: Need a valve that can handle pressure on the outlet . . .
RE: Need a valve that can handle pressure on the outlet . . .
RE: Need a valve that can handle pressure on the outlet . . .
There's only so much force you can get out of an 8-watt or 12-watt solenoid coil!
Burkert and Spirax Sarco both sell a small threaded air piston-actuated Y-pattern valve. Double acting and spring return versions are available. May be physically smaller and will probably be cheaper than the actuated Whitey valve option- if you have instrument air available.
Kitz amongst others has a small commodity 2pc threaded ball valve with close coupled actuator (CSAUTE).
RE: Need a valve that can handle pressure on the outlet . . .
1. If you want to use a solenoid valve, you have a possible solution in a solenoid valve, universal type,and 3/2, where one port can be plugged, the two others giving a normal 2/2 on/off action. Theese exists (still, I believe), see below at the Norgren (Herion series from Germany) site:
http://
Note the large size and wattage for the solenoids!
2. Secondly you could of course use a normal 2/2 solenoid valve with forced lifting, plus a disc-type checkvalve at the downpressure side to avoid lifting if pressure direction reverts. To obtain flow both ways, however, you have to use two of theese solutions in parallell, working in opposite directions.
3. The conclusion is as answered above: cheapest and best is most often to use a ball valve. Or, as I have found on many occasions, a high quality y-type globe valve with pneumatic actuator and spring return.
RE: Need a valve that can handle pressure on the outlet . . .
Just to make sure I understand correctly, for the Norgren valve in option 1 . . . I could, for example, block off port 1 and connect ports 2 and 3 for normally closed operation.
Can I then pressurize either port 2 and port 3 without leakage (say 100 psig on port 2 and 0 psig on port 3 OR 100 psig on port 3 and 0 psig on port 1). What is it about the design of this valve that prevents leakage regardless of which side is pressurized?
RE: Need a valve that can handle pressure on the outlet . . .
RE: Need a valve that can handle pressure on the outlet . . .
Arrow symbols pointing in both directions meaning flow or pressure for the whole given range in both directions.
1,2, and 3 representing ports. Small rectangle to the left symbolizing solenoid operation, and left square showing flow and connections when solenoid is operated. In the same way right square showing situation when the valve is operated by the spring return, spring symbol to the righthand end.
No secrets: sufficient spring force to close, and strong enoough solenoid to operate to 'open' (opposite) situation, and good mechanical construction.
I know the valve well, no negative effects if you block one port, more important to remember the general restrictions for use of fluids with solenoid valves: temperature limits, compabillity to sealings and other materials, viscosity limits, no dirt or residues - only clean fluids, no fluids or situations where (rest) fluid can dry up and give gluing or abrasive effects.
But yes: the price and size is in such a range that that you will want to check cheaper technicl solutions first.
Typical (of many possible) uses for this valve (as 3/2): actuator operation for large pneumatical actuators, where large flow and fast opening or closing is required. Can also be used in series as redundant emergency shut down for actuators.
The solution compeats against pilot operated solenoid valves with several advantages: dependabel and robust construction, probably liftime length, closing down to zero bar G, and even going very far into the vacuum range, and the bi-directional flow possibillity.