Generator RTD reading difficulties
I am having a strange noise(?) problem with measuring some 3-wire 10-ohm copper RTDs installed in a generator.  When the generator is not running, the rtds read fine, but when the generator is running, the stator winding rtds read noisily, but the bearing rtds read fine.  I am using shielded wire from the rtd terminal box to my datalogger.  The stator RTDs flucuate +/- 10-20 deg C from reading to reading.  I have switched cards in the data logger, grounded one leg of the RTD, moved the ground on the shield wire, all with no effect.  I have discussed this with the datalogger manufacturer and they have no solution for me.  Has anyone encountered this problem before?
RE: Generator RTD reading difficulties
its been a long time, but i recall fusable grounding disk on the terminal strip, just behind the terminal screws and if thet were not there having problems with pen recorder
A rogue ground connection somewhere at the field end? There should only be a ground for the shield at the quiet end (i.e. chart recorder, DCS, etc). Check the RTD itself for a ground as well as the screen.