Are VFD motors more likely to cause electrical arcing in bearings?

Are VFD motors more likely to cause electrical arcing in bearings?

Are VFD motors more likely to cause electrical arcing in bearings?

(OP)
I was reading up on failure modes for bearings and saw pictures of the fluting that results from arcing across balls & races. I have heard that VFD motors are more likely to have this problem than single speed motors? Is this true? If so, why?

RE: Are VFD motors more likely to cause electrical arcing in bearings?

It is very true. See the "neighbour" thread on ultrasonic in bearings. The electrical phenomenon is being discussed at some length there. I have put together a short paper that can be found at http://www.gke.org/beppe/files/Bearing%20currents%20on%20one%20page%201.pdf The goal was to put everything on one page. So it is rather condensed.

There is a pdf presentation available at http://www.gke.org/presentationer/files/EDM%20Physics%20and%20Reality%201.pdf

 

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Are VFD motors more likely to cause electrical arcing in bearings?

Adding a tidbit of information from our experience.

We found out almost from the beginning using VFD's you didn't want to put more than two on single transformer. We had a serious problem when we converted fan motors on a 7 cell cooling tower to VFD. We wiped out four motors until the problem was diagnosed and resolved. All our VFD's in this service are now on separate feeds. There is also some type of filtering system at substation feeding the cooling towers,  Separating the drives was a very expensive problem to correct..  I can only assume that it payed off as there are still VFD drives on the cooling towers.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources