How does the Delta Wye Switch Work? Help!
Dear Gods of Electrical Motor Theory,
I am just a lowly automotive/manufacturing guy most humbly petitioning you, the Gods of Electrical Motor Theory, to grace me with your knowledge on how the delta wye switch works.
Yes, I have searched Google. I have searched this site (you guys understandably gloss over it). I have searched high and low but can not find the answer to my question. I recognize my own electrical stupidity is probably hindering me.
If anyone had a few minutes, I would be most grateful.
I just read this
ht tp://www.m msonline.c om/article s/wyedelta -in-perspe ctive.aspx
My question is, does the delta/wye extend the torque range in a VFD 3 phase motor? How? and most importantly, why?
From the Haas website:
On-The-Fly WYE-DELTA Switching
Many Haas VMCs feature the Haas Dual-Drive
system, which consists of a dual-winding motor –
Wye and Delta – and an electronic switch to change
between the two windings. Selecting the best
winding for low-rpm cutting and the best winding
for high-rpm cutting yields higher torque over a
wider rpm range. The Haas Dual-Drive system also
provides constant horsepower over a much wider
rpm range, and on-the-fly winding change
provides the wide power range necessary for
constant surface speed cuts.
David
I just read this
ht
David
RE: How does the Delta Wye Switch Work? Help!
Normally a delta-wye transition is used only during motor starting. Windings connected wye see less voltage than when they are connected in delta, so the current is reduced AND the torque is reduced. Torque is roughly 1/3.
I've never heard of switching between wye and delta when the motor is running under load.
But with a modern VFD, you will have much better control over the motor over the full range of motor torque than you would ever get with by switching between wye and delta.
It would help if we knew what the application was.
If Haas is using this (see above quote and link) they why are they using it? Or, is this a bogus sales pitch? They say they switch "on-the-fly" to provide constant power over a wider range.
I will try to post a screen shot of the graph they publish.
David
www.kirkhammotorsports.com
A VFD can vary the voltage and frequency of its output to provide virtually any torque (within the motor's and drive's capabilities) at any speed. Anything that could be accomplished with the wye-delta switching could be accomplished more effectively with a properly sized and rated VFD with the right power supply.
It does seem a bit like a marketing gimmick, but I'm certainly not an expert, especially since I have no idea what you are trying to accomplish with this motor.
In standard industrial motor applications (fans, pumps, etc), I've never heard of switching between wye and delta while the motor is running under load.
Sorry, application, my fault. I should have stated that right off.
I am looking for 2 things. One is knowledge on such subjects as the mystery of electrons.
The other is I am fantasizing about retrofitting a large 5 axis mill I have and I am wondering if I can spread the torque curve, as Haas says they can, on the spindle.
In a milling application, you need high torque at low speeds (100-500 for cutting steel) and high rpm's (15,000 or so) to cut aluminum--but you need every speed in between as well. In a lathe, you need to cut at constant surface feet so you can start a cut at a low rpm on the OD and finish in the middle at a much higher rpm--all the time loading the motor.
Yes it can increase the torque. It is essentially a two position reduced voltage system. Theoretically it does not change the speed as that is set by the frequency.
Your applications would benefit greatly from a vector drive. It would likely benefit nothing from wye/delta.
On a different note: Whatever happened with the Electric Kirkham?
Keith Cress
I am curious as to why Haas does it then? Marketing? (Haas uses a vector drive, so why do they do the switch?).
Electric Kirkham is a side project that is currently in an engineering black hole--the place from which no product escapes! (At least without a massive tirade from the CEO). Actually, I am finishing up another massive project right now that has almost sucked the life out of me.
http://clubcobra.com/forums/showthread.php?t=85278
After you read that thread, you will realize why my thoughts are with an old 60 x 60 x 60 5 axis mill that needs a ton of work to run again. I would love to make some crazy parts on it. I would like to get the best performance out of it that is possible (for a reasonable amount of money).
David
By the way, delta and wye are two methods of connecting the same windings, not two separate windings.
If there are two separate windings, then anything is possible. We would need to know a lot about each winding before we could make any suggestions.
Bill
"Why not the best?"
Jimmy Carter
I understand the delta connection refers to a "triangular" shaped connection of each of the 3 phases (with a wire between each of them) and the wye refers to each of the ends of the 3 phase windings all connected together at one point. Somehow this is related to series and parallel connections, (between the phases) but that relation is not somehow clear in my mind how this causes a rise/drop in voltage, current, torque...
That is the real question here.
As I did the searches here and on the web, everyone kept talking about the different connections (delta/wye) being used for different input voltages...that is not what Haas is doing as they use a VFD??? Am I right? So, why are they doing it (on the fly switching)? I can't imagine they would simply lie in their advertising.
So, what is it that drives torque in a motor?
Something tells me Haas would not do it if it were not valuable as they could be easily outed by an EE. (But not so easily by a ME, it seems :) )
David
This is a technique for running VFD driven motors above base speed. If a motor rated at 230 volts is run above base speed, the volts can not increase to maintain the "Volts per Hertz Ratio". At 3600 RPM, an 1800 RPM motor could be supplied with 460 volts with a corresponding increase in power. Some manufacturers use 460 volts and a VFD to gain 200% to double the power out of a motor. (200% voltage and 200% frequency and speed at normal torque).
The wye delta switching technique allows the effective voltage rating of a motor to be lowered to extend the operating range at speeds above base speed.
A motor rated at 10 HP at 1800 RPM would deliver 17.3 HP at 3117 RPM.
Bill
"Why not the best?"
Jimmy Carter
When I read it though, I though they may be using a 2-speed 2-winding motor. Basically, have something like a 400rpm winding and a 3600rpm winding.
In either case, you should be able to get reasonable performance from a fixed speed motor with a open loop flux-vector type VFD. If that isn't good enough, a motor with an encoder providing feedback to the VFD would work.
I would not call a 2-speed 2 winding motor an "on-the-fly" delta/wye switch.
Pretty much all CNC spindle motors these days have encoders on them for the rigid tap and spindle orient commands.
Anyway, what am I missing? (Beside brains).
David
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
You have two winding schemes so that the same V/Hz and speed occurs with two different supply voltages. Why does switching them allow any change to speed, or for that matter torque? How would this be any different from getting a 240V motor and running it up to some higher voltage without the complexity?
Keith Cress
I remember your postings about a year ago on electric cars.
Now, the Wye/Delta switch as such is not very problematic. But I think that the application you seem to think about is a bit extraordinary. Have I got it right when I think that you want to have the motor in Wye for high torque up to a certain speed and then switch to Delta so that speed can be taken up furter to 1,73 times base speed? If so, it still sounds perfectly normal.
You would probably do this so you can get full motor power over a larger speed range without having to oversize the inverter. If the VFD size reduction outweighs the complexity is something one has to think about.
The problem seems to be that you want to do it on the fly without causing any torque shocks in the shaft. That would be impossible if you are using an electro-mechanical switch.
If you use solid state switches instead, it seems to be quite easy. You will need a fast frequency inverter with a specially designed control program that:
1. Disconnects motor from inverter.
2. Measures back EMF and adjust new output voltage to have same frequency, amplitude and phase as existing back EMF.
3. Opens the Wye switches.
4. Closes the Delta switches.
5. Connects motor to inverter.
The whole thing could probably be somewhat simplified. But that seems to be the general idea.
It is necessary to adjust the inverter output so it takes both new voltage level and the 30 degree phase shift in back EMF into account. There will probably be a short (a few milliseconds) paouse in torque, but you can probably live with that. It is much better than having a torque shock like the one you get from the phase and voltage mismatch if you do not do it right.
Does this sound like the thing you are telling us about?
Gunnar Englund
www.gke.org
I can not imagine someone (Haas) doing something (on the fly switch) they could be called on the carpet for.
Gunnar, I thank you, as always, for your help :)
David
You stated the technique is "so baroque that anyone embarking on it will be sorely disappointed." I am reminded of Bach, Handel, and Scarlatti. Their music is far deeper and more complex than can be appreciated with a cursory glance. Hundreds of years after their music was written, it continues to grace our existence. Perhaps there is merit in "baroque" ideas.
David
I certainly wouldn't go this route.
But to each his own.
And... Presently I'm listening to Beethoven - Symphony - No.5 Allegro Con Brio You know: DAH-DAH-DAH--Dahhhhh
Keith Cress
Normally the power of a motor flat-lines when running above base speed.
If you can continue to increase the voltage to maintain the V/H ratio the power will increase above base speed. But you know that.
But, if you can't raise the voltage, how about dropping the voltage rating of the motor.
Example;
Motor rated at 230 volts.
Power maxes out at 230 volts/60 Hz.
Now connect in delta and drop the inverter output to 133 volts at 60Hz. The motor will draw more current but will produce the same power at the same speed. Now run the inverter up to 230V/104 Hz and 173% of base power. More power and speed out of the same motor.
Bill
"Why not the best?"
Jimmy Carter
Keith Cress
Usually you use a gearbox for that. But if you try to shift gears while turning a circular surface, you will get nasty traces in that surface. I can imagine that some kind of a complicated clutch can do the shifting without stopping the lathe. But it sounds expensive and complicated.
If you want full torque and full speed out of a drive system, it has to be diesigned for maximum spedd times maximum torque. By using some kind of gear (my guess is winding switching in this case), you can have full torque at low speeds and full speed at low torques and still use a drive system that is, perhaps, one fourth of what you need if you design for "the whole square" so to say.
Gunnar Englund
www.gke.org
I always liked Bach more than Beethoven.
Thank you all for your responses!
David
Gunnar Englund
www.gke.org
I is late and I am still awake :)
Gunnar hit the nail square on the head. The switch must be extremely smooth as gears introduce vibrations in the milling head and leave witness marks (traces) on the part that is being machined. Such marks can ruin a part (I am thinking of a custom steering rack and pinion I made only yesterday out of 300 Maraging steel.)
I am confident this works. Now, I ask the electric motor theory gods to answer the ultimate question...How? Why?
David
Gunnar Englund
www.gke.org
Yes, you did!
I was dreaming more about "how" the actual electrons are moving in the wires and how this affects a given system...a question like you would ask your physics professor in class and drive all the other students crazy (who are only trying to memorize equations) as your professor delights in pontificating on the process.
I guess I should not drive the engineers on this site crazy with such ruminations.
Thank you all so very much! You have been a great help.
David
Let me see if I can amplify skogs' and waross' comments to make it clearer.
Very basic 3-phase AC circuit analysis:
For a Wye-connected load:
Vphase = (1/sqrt(3))*Vline
Iphase = Iline
For a Delta-connected load:
Vphase = Vline
Iphase = (1/sqrt(3))*Iline
So when you switch the motor from Wye to Delta, you bump up the voltage to the phase by a factor of 1.732, but reduce the current through the phase by the same factor.
The higher available phase voltage permits higher speeds, but the reduced phase current means less torque capability. As skogs says, this is equivalent to a change in mechanical gear ratio of this same factor. Delta connection provides a "higher gear".
As a possibly relevant aside, the prototype Tesla electric sports cars had a 2-speed gearbox. Unfortunately, these got ground up very quickly in endurance testing (my guess is that they were not up to handling full torque at zero speed, which a vector-controlled induction motor can provide, but an internal combustion engine cannot). The production version has a single-speed gearbox, and Tesla says it is now using electrical means to get the full torque/speed range. I wonder if they are pulling the Wye/Delta switch?
Curt Wilson
Delta Tau Data Systems