wye delta transformers
wye delta transformers
(OP)
Tell me why I cannot swap a 1000kva wye delta with a 1000kva delta wye (no neutral ground) transformer. Thanks for you help
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: wye delta transformers
Regards
Marmite
RE: wye delta transformers
K2ofKeyLargo
RE: wye delta transformers
Which is existing and which is proposed?
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: wye delta transformers
RE: wye delta transformers
A few issues:
Current distribution on the primary,
Switching surges,
Power back-feeds when a primary phase is lost,
Common practice and common utilization voltages,
Power transmission or distribution,
The number of primary conductors,
Ground fault scenarios.
A final generalization;
Vague questions such as this are often suspected to be homework and may be red flagged.