A project was done in house, where they had to install a 480 V - 3 phase tank heater ( I am not sure of the KW rating ), in a spare tub, which is a soft start.
I believe it normally draws 92 amps....or very close to that.
The main MCC breaker tripped, and someone wondered if it was because the soft start caused excessive amperage draw, when it started. I said not likey. On an electric baseboard heater for example, if you cut the voltage in half, the current also drops by 1/2, and you have 1/4 of the wattage. This should also be applicable on a 3 phase heater as well, I would assume ? Its a resistive load, so 92 amps, should not peak, or vary....its either on or off....correct ?
I believe it normally draws 92 amps....or very close to that.
The main MCC breaker tripped, and someone wondered if it was because the soft start caused excessive amperage draw, when it started. I said not likey. On an electric baseboard heater for example, if you cut the voltage in half, the current also drops by 1/2, and you have 1/4 of the wattage. This should also be applicable on a 3 phase heater as well, I would assume ? Its a resistive load, so 92 amps, should not peak, or vary....its either on or off....correct ?






RE: 3 phase Heater on soft start .
I don't know what you're refering to as a soft starter, but I'll assume it a controller with an adjustable "On" ramp. It that ramp time is short enough, you might see inrush in excess of your CB rating. Extend the ramp time some & see what happens
Ed
RE: 3 phase Heater on soft start .
Not sure how your "soft start" works -- is it a wye-delta transition starter, or autotransformer starter, a VFD-style soft starter, or some other reduced-voltage device?
You're right about how the heater should act at reduced voltage.
Is your 480 system grounded, is it 3-wire or 4?
From the amps you quote, it's about 75 KW.
Feed us some more data -- this could be anything from a ground fault to a wiring error...
Good on ya,
Goober Dave
RE: 3 phase Heater on soft start .
RE: 3 phase Heater on soft start .
RE: 3 phase Heater on soft start .
I'm familiar with the AB devices. Here are some thoughts.
If the heater is purely a resistive one (not using induction), it should work.
Fangas is right in that there will be an inrush due to lower resistance at lower temperature when starting, but it shouldn't be as severe as a light-bulb filament (temp difference from cold to hot isn't as great).
What's the trip setting on the CB that is tripping? Does it have ground fault protection? Since your main circuit breaker is tripping, it seems that a ground fault is possible.
Let us know what you find out!
Good on ya,
Goober Dave
RE: 3 phase Heater on soft start .
Are there any transformers between the controller and heaters?
How are the heaters configured? Specifically, are they in a Wye configuration with the center neutral?
Ed
RE: 3 phase Heater on soft start .
Engineer said he took and ohm reading between phases and all seemed balanced, but that does not verify our insulation factor either.
RE: 3 phase Heater on soft start .
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: 3 phase Heater on soft start .
If I remember correctly, time delay fuses will allow 500 % of the rating for 10 seconds. So, a ground , ( if ground fault protection is provided on the breaker,) is definitely an option.....you think ?
Or possibly a short between windings ?
RE: 3 phase Heater on soft start .
Keith Cress
kcress - http://www.flaminsystems.com
RE: 3 phase Heater on soft start .
The resistance of heating elements can be very dynamic. They'll have both a hot and cold resistance.
If (for simplicity) an element has a cold resistance of 1 Ohm and you apply 100V to it, it will draw 100A initially. If it has a hot resistance of 2 Ohms, it will draw 50A when it warms up.
A 100W lamp at 100V will draw 1 A, showing a hot resistance of 100 Ohms. If you take that same lamp and measure its resistance cold, it will appear almost like a short.
Your elements may not be as dynamic, but they will change. So yes, for some period of time, under full voltage, your elements can draw more then 92A.
That's where Jraef was going. If your control is set up for current limit, it will only throttle back the voltage when that limit is met. And might be set too high for your load, or not fast enough to respond. That's why he recommended making sure you're setup for a voltage ramp.
Itsmoked, was refering to the fact, if you have miswired anything, such you have some parallel elements where there isn't supposed to be some, your resistance will be reduced even further.
Ed
RE: 3 phase Heater on soft start .
Keith Cress
kcress - http://www.flaminsystems.com
RE: 3 phase Heater on soft start .
Definitely another possibility. Some soft starters, especially digital ones such as the AB SMC Series, might take a half second or so to initialize before they can begin limiting current. Normally not a big deal in a motor circuit. In addition, AB soft starters have a feature called "Kick Start" which is supposed to be used to "break free" a motor load that might be stuck due to excessive friction or icing etc. If that feature is enabled, it does NO control of voltage (or current) for the first few seconds (adjustable from .2 - 2 seconds), then it drops down to the initial ramp settings In a heater, that may be long enough to make the breaker trip or fuses blow.
Another issue: you didn't say which of the AB SMC products it is. In that size range, it could be the SMC Flex, which has built-in bypass contacts. In a purely resistive load, ie.e no inductive properties, the soft starter may interpret the current profile as if it is a motor that is getting to full speed very quickly and it will override any ramp settings, going to full voltage almost immediately and closing the bypass contactor.
Remember, you have taken a device intended to be used on a motor application and are using it on something that it was not designed to work on. It CAN work, but you must be vigilant on making sure it is used correctly.
The problem is in the soft starter setup IMHO and it is not likely a bad component either. If it were, the soft starter would see that and fault.
By the way, if the soft starter is working properly, a shorted load would NOT likely cause the current spike you are seeing until AFTER the soft starter was done ramping because the current is going to be artificially limited by the soft starter. That is something seen in motor applications all the time; people discover they have a problem in the motor when they add a soft starter because the current limitation allows the effects to last long enough to be seen, whereas when they started across-the-line, it was happening too fast.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: 3 phase Heater on soft start .
Like all good main't, they were a bit lazy and "F'in Mangas" As in "That F'in Mangas (My last name), I'm gonna kill him" quickly got shortened to Fangas.
Ed
RE: 3 phase Heater on soft start .
I would check the rated voltage of the heaters, the connections (wye or delta) and see if any drive experts can suggest why a soft start won't drive a resistive load. The slight extra current when cold is insignificant compared to the starting current of a motor.
Another strong possibility is that the soft start is bad. That may be why it is 1) still available, and 2) not cannibalized or removed from the MCC tub.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 3 phase Heater on soft start .
OK Ed.
I must have been thinking of Furnas.
Keith Cress
kcress - http://www.flaminsystems.com
RE: 3 phase Heater on soft start .
Thanks for the help ! This opened up quite a discussion on controlling heaters through a soft - start.