to find out locked rotor current &load factor

to find out locked rotor current &load factor

to find out locked rotor current &load factor

(OP)
Hello,
Can anyone help me to find out the rated current/locked rotor current & load factor of a 15KW motor which is connected to 415V ac.Estimated full load current & maximum demand are 26Amps.Load diversification=.06.Thanks in advance.

RE: to find out locked rotor current &load factor

Rated current = Full Load Amps = FLA.  This should be on the motor nameplate.  Locked rotor current should be indicated on the nameplate by a Code Letter (if NEMA motor).  

Load factor, as I use the term, is dependent on the load.  If you are referring to Duty Cycle, that should also be on the motor nameplate.  

I have no idea what Load Diversification is referring to.  

If this is a new(ish) motor, you may be able to get a motor data sheet from the motor supplier.  

 

RE: to find out locked rotor current &load factor

Hi veronica19978
As dpc already said "NEC[NFPA-70] art.430-7 b Locked-Rotor" indicates Code Letters for Usual Motor Application. The manufacturer has to indicate this letter in order to appreciate the locked rotor current [there are 19 letters from A to V and  kVA per Horsepower with locked rotor is tabulated].
The load diversification is the ratio between total installed power and maximum required power.
For a single motor connected to a single branch the load diversification is also the load factor.
So, as 26 A is close to the FLA then  26/.06=433 A is very large current for rated current, in your case, I think.
Usually powerfactor=0.8-.9 and efficiency 0.6 to 0.9, then max.Irated may be= 1000*15/415/sqrt(3)/.8/.6=43.5 A
In this case the diversity factor may be 26/43.5=0.6 approx.
For motor manufactured according to IEC 34-12 usually the locked rotor current is expected to be 6.5-7.2 time the rated current [for 15 kW induction squirrel cage motor 1000-3000 rpm].
Regards
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources