Seismic Loading
Seismic Loading
Seismic Loading
How do I go about designing for seismic loading? Our normal calculation for designing a tank uses the 4 x the bending moment x 1000 divided by pi x diameter^2 is this correct way to go about this? We state that this is designed to 0.1g, is this correct? if so how does changing the g change the calcs? also how does designing to UBC 94 zone 1 change things? I would be greatful for any assistance thanks
RE: Seismic Loading
What kind of tank?  How is it supported?
If it's a flat-bottom vertical steel tank, you could design to the seismic provisions of API-650 or AWWA D100.
If it's not a steel tank, or not in the US, you may find other applicable tank standards.
Otherwise, check into ASCE 7.  It may be kind of a mess to extract an actual load out of it, but it does include tanks as "non-building structures".
As to the "4 x the bending moment", where does the bending moment come from?
If you're actually required to use UBC-94 or IBC, check very carefully to see if they just refer back to ASCE 7.  And note that for certain tanks, ASCE 7 refers to tank standards.
RE: Seismic Loading
Thank you for your reply
It is a flat Based GRP tank and it is not in the US. The bending moment comes from Wieght of the full tank/10 times the Height of the tank/2
We normally design to BS4994 which doesn't really have anything on Seismic Loading. in the UBC code there are some formulae but I am not sure where they fit into our calculations.
RE: Seismic Loading
You might want to get a structural engineer involved that knows and understands seismic codes and forces.
RE: Seismic Loading
I have been given this equation to work to
R(T) = aN*RD(T)*P*t
Where aN = 2.0 m/s-2 (nominal acceleration for zone 1b and class C building)
RD(T) = Spectrum for Site S2
P = Damping
t = topographic Coefficient equal to 1
There are 2 graphs for RD(T)
Top graph(The graph is in French and says Composantes Horizontales)
y axis is RD
x axis is T
with 4 Lines (S0D, S1D, S2d, S3D)
with respective equations R=1.12/T*(2/3); R=1.36/T*(2/3); R=1.60/T*(2/3); and R= 1.86/T*(2/3)
So I take it that for site S2 I would use the line S2D (R=1.60/T*(2/3))
Bottom Graph (Says Composante Verticale)
y axis is RD
x axis is T
with 2 Lines bottom line (S0D eq. R=1.12/T*(2/3)
Top line (S1D, S2d, S3d eq. R=1.36/T(2/3))
So I am getting there now what I need help with is
1) how do I work out the damping
2) What value should I take for T? from this value I could read of the value of RD from the graphs
3) Would I then take the 2 graphs seperately and add this to my longitudinal and circumferential loadings I have already calculated? Or would I combine these graphs to get a single value for RD(T)?
4) Would this calculation be sufficient? Or would I need to examine any further calculations?
RE: Seismic Loading
API 650 deals with this directly (including sloshing in the tank) and it refers at times to ASCE 7.  The last few ASCE 7's (since 1998, I think) don't use zones any more.  It's based off of ground acceleration maps.  Unfortunately for you, the only maps included are for the U.S. and its territories.
If you "heard" it on the internet, it's guilty until proven innocent. - DCS
http://www.eng-tips.com/supportus.cfm