High Voltage Room Airconditioning
Is there any rules and regulation regarding the installation of air conditioning unit which feed by chilled water system? I am aware for possible water drip off and water leakage on the piping. If so is it applied also to tranformer room and low voltage room?
RE: High Voltage Room Airconditioning
Not allowed. Keep the water (and possible condensation that goes along with it) out of the electrical rooms. If the room needs cooling, set your fan-coil unit outside the room and duct some cold air in.
NEC 110.26(F)(1) gives specifics.
Good on ya,
Goober Dave
IMC requires emergency drain pan under unit with drain pan overflow alarm.
We typically use a double containment pipe for the condensate piping, and a drain pan under the CHW piping, piped to the condensate drain.
One more point: Check with AHJ. In one locale, I was forced to take all piping and cooling from the room, the only thing he would accept was a sidewall diffuser across from the electrical gear.
Good on y'all,
Goober Dave