Arc flash protection VS Differential protection

Arc flash protection VS Differential protection

Arc flash protection VS Differential protection

(OP)
Hi all!

In a 5 kV switchgear, would a busbar differential protection help reducing the Arc Flash Hazard?

I think yes. Your comments are welcome.   

RE: Arc flash protection VS Differential protection

Anything that reduces interruption time will reduce arc flash hazard.  If the busbar differential trips a main breaker in the switchgear, however, you still have to consider the interruption time for a fault in the main breaker compartment that isn't cleared by the bus differential.
 

RE: Arc flash protection VS Differential protection

Yes, it's generally a big help due to faster clearing times.  As jghrist indicates, you have to carefully determine the differential zone and determine where faults might not be cleared by a bus differential operation.  It helps if there is an upstream transformer differential zone that can be overlapped with the bus diff.  


 

RE: Arc flash protection VS Differential protection

For my pinion , both of them are good and important.
Isn't versus. One add second.
my 0.02$
Regards.
Slava

RE: Arc flash protection VS Differential protection

I agree that diff. protection will help, as previously posted, however, if your primary concern is arc flash why not use an optical arc detection system designed for this purpose. It would probably be easier to install since CT inputs from each breaker are not required. Just a thought,

suhag

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources