Sprinkler heads In Large Rooftop AHU

Sprinkler heads In Large Rooftop AHU

Sprinkler heads In Large Rooftop AHU

(OP)
Has anyone ever heard of or seen sprinkler heads installed in a large rooftop unit with a side attached service space with large plenums.

I understand having heads in the service spaces, and large plenums,  but having them in each section of the unit, ie: Coil section and fan section?

Any Questions or comments?  

For instance if you had a rooftop unit large enough to get inside would you provide sprinkler heads inside?  Does NFPA 13 cover this instance?

Cheers!

RE: Sprinkler heads In Large Rooftop AHU

Not normally

IF it was an entire room on top of the building with hvac yea maybe

Now if someone one is requireing it insurance, company policy or the such than yea I guess stick them in.  

 

RE: Sprinkler heads In Large Rooftop AHU

Its a piece of noncombustible equipment. Sprinklers are not required by NFPA 13.

And if an insurance company was wanting it, I would challenge it, especially if the RTU is located in a climate subject to freezing.

RE: Sprinkler heads In Large Rooftop AHU

I have seen automatic sprinklers in these spaces when the construction is combustible and I have seen sprinklers in these spaces at textile facilities (primarily due to the lint accumulation issue) even when the roof top "units" are non-combustible.

NFPA 13 does not specifically exclude or omit the requirement for sprinkler protection for this instance. I would be comfortable with these "units" being unsprinklered as long as the construction is completely NC or minimal combustible and there are no combustible contents (including lint accumulation).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources