Sprinkler heads In Large Rooftop AHU
(OP)
Has anyone ever heard of or seen sprinkler heads installed in a large rooftop unit with a side attached service space with large plenums.
I understand having heads in the service spaces, and large plenums, but having them in each section of the unit, ie: Coil section and fan section?
Any Questions or comments?
For instance if you had a rooftop unit large enough to get inside would you provide sprinkler heads inside? Does NFPA 13 cover this instance?
Cheers!
I understand having heads in the service spaces, and large plenums, but having them in each section of the unit, ie: Coil section and fan section?
Any Questions or comments?
For instance if you had a rooftop unit large enough to get inside would you provide sprinkler heads inside? Does NFPA 13 cover this instance?
Cheers!





RE: Sprinkler heads In Large Rooftop AHU
IF it was an entire room on top of the building with hvac yea maybe
Now if someone one is requireing it insurance, company policy or the such than yea I guess stick them in.
RE: Sprinkler heads In Large Rooftop AHU
And if an insurance company was wanting it, I would challenge it, especially if the RTU is located in a climate subject to freezing.
RE: Sprinkler heads In Large Rooftop AHU
NFPA 13 does not specifically exclude or omit the requirement for sprinkler protection for this instance. I would be comfortable with these "units" being unsprinklered as long as the construction is completely NC or minimal combustible and there are no combustible contents (including lint accumulation).