Meaning of CT 1200/5

Meaning of CT 1200/5

Meaning of CT 1200/5

(OP)
Hi,

When the current transformer is label 1200/5:
1. Is that means primary current that not exceed 1200A, the transformer will operate in linear region?
2.If the primary current more than 1200A, then the transformer operate in saturation region?

RE: Meaning of CT 1200/5

You have to know the "rating factor" to know maximum continuous current. RF = multiple of rated current (ratio) that the CT can handle continuously without overheating. It's based on a given ambient, for instance in the US, it's generally based on a 30C average ambient over a 24 hr period.

RF also defines the upper limit of the metering accuracy class.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources