We know that motor peak inrush current (first cycle) can vary randomly based on the phase angle of the voltage at the time of closiong.
Let's say I start the motor many times and each time record the single highest magintude peak (either polarity, any phase) for each start.
Assuming ideal conditions (simultaneous contact closure on all 3 phases without bounce, balanced voltage, no motor assymetries), what would you estimate the variability of these recorded numbers as as a result of random variation of voltage phase at time of closing?
From a simple R/L circuit model, I estimated around 6% variability (max peak minus min over average) at pf = 0.15. Spreadsheet attached (don't look at the cell formula's... they are uglier than they need to be). Seems like surprisingly low variability. Maybe I made an error?
What do you estimate?
Let's say I start the motor many times and each time record the single highest magintude peak (either polarity, any phase) for each start.
Assuming ideal conditions (simultaneous contact closure on all 3 phases without bounce, balanced voltage, no motor assymetries), what would you estimate the variability of these recorded numbers as as a result of random variation of voltage phase at time of closing?
From a simple R/L circuit model, I estimated around 6% variability (max peak minus min over average) at pf = 0.15. Spreadsheet attached (don't look at the cell formula's... they are uglier than they need to be). Seems like surprisingly low variability. Maybe I made an error?
What do you estimate?
=====================================
Eng-tips forums: The best place on the web for engineering discussions.






RE: How much random variation in motor inrush peak current due to closing
RE: How much random variation in motor inrush peak current due to closing
This particular chunk - we recorded a multitude of starts. I was presented summary data consisting of a single number for each start - the highest peak on any of the phases during that start. There was considerable variability in those particular numbers. I did an analysis (attached) to see what is expected variability under these particular assumptions (balance etc). The results suprpised me (low variability). I figure they might suprise others as well. I want to make sure that particular analysis is correct. If so, it helps us BEGIN to answer some questions I have been asked like: How many starts do I need to do to capture the worst case? If I record 3 starts and want to set my breaker comfortably above the behavior observed during those starts, how much additional margin should I include to allow for closing time variation (yes, there is a ton of other margin to be accounted for, including the balance assumption which I think will be a big factor in explaining the variability... but it is not the question here).
So the question is unchanged, do you agree with my analysis/conclusion as described in my first post, under the assumptions given ?
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: How much random variation in motor inrush peak current due to closing
When you start a motor one phase is always in a position to give a large inrush.
I couldn't load your spreadsheet but I agree that there will be a relatively small variation between the maximum currents of the highest phase.
The ripple of a three phase bridge rectifier is much less than the ripple of a single phase bridge rectifier. I believe there may be a similarity.
Bill
--------------------