was called to a school today to investigate a fault on a heater unit. It is realatively simple set up, it consists of a water heated heatextchange and a single phase capacitive start motor, with a variable resistor set at 50 ohm in series with the phase conductor, i presume so the speed can be alterd depending on the size of room it is insalled in. also there is variouse temp sensors.
On inspection of the unit I found that the variable resistor had burnt out and gone open ciruit. so we aquired a new one and replace the resistor and tested the unit. we further then found that the motor had failed.
In testing the motor i tested for any earth fault with IR tester and got high good reading, I tested the resistance of the start winding and got an acceptabe low result, I tested the run winding and got open circuit indicating that thier was a breack in the winding some were,
Why would the variable resistor failing cause the winding in the motor to go open circuit.
I have had the motor sent to be re-wound. But i would have liked to know why the resistor failing would cause damage to the motor.
Thanx for any advise
was called to a school today to investigate a fault on a heater unit. It is realatively simple set up, it consists of a water heated heatextchange and a single phase capacitive start motor, with a variable resistor set at 50 ohm in series with the phase conductor, i presume so the speed can be alterd depending on the size of room it is insalled in. also there is variouse temp sensors.
On inspection of the unit I found that the variable resistor had burnt out and gone open ciruit. so we aquired a new one and replace the resistor and tested the unit. we further then found that the motor had failed.
In testing the motor i tested for any earth fault with IR tester and got high good reading, I tested the resistance of the start winding and got an acceptabe low result, I tested the run winding and got open circuit indicating that thier was a breack in the winding some were,
Why would the variable resistor failing cause the winding in the motor to go open circuit.
I have had the motor sent to be re-wound. But i would have liked to know why the resistor failing would cause damage to the motor.
Thanx for any advise





RE: single phase motor proplem
RE: single phase motor proplem
Roy
RE: single phase motor proplem
It could be that the system was originally designed to be used with a split-phase or a shaded pole motor, and at some point the motor failed and was replaced by the cap-start one, but that would be an inappropriate replacement. Unless there is some kind of special motor out there that I am unaware of.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: single phase motor proplem
What i think may have happen is that a fault has occurred in the motor causing a overload, Because of the 50 ohm resistor this would have kept the over load to low to blow the fuse in the spur unit and cause the actual resistor to heat up like a heater element and burn out. That's wot i think but i may be wrong, These heaters are pretty old unit probable installed in the 60s.
Thanx for any advise. I find this site very usfull and educational. As a lot of things mention on here i have come up agaist in the past in my job but never had a proper explanition as to the root cause of the proplem or failre.
RE: single phase motor proplem
I've worked on a wide variety of motors and I can't say I've ever seen one with a resistor...