Torsional Stress on a Channel "[" section
I have to check a channel section which is sub to torsional moment.
However, I can't remember the equation for the calculation of shear stress because I have left school for a long time.....
I am wondering whether anybody remembers the equation....
Thanks!!!!
Thanks!!!!
RE: Torsional Stress on a Channel "[" section
For a solid bar:
Tau = Mt/J
Where M = Applied Torque
t = Member thickness
J = Torsion constant = (bt^3)/3 for b/1 >= 10
or
For a hollow section:
Tau = M/(2At)
where A = Area enclosed by the centre line of the hollow section = (b-t)(d-t)
HOWEVER the torsional effects on an "open" section are more complex those for a solid bar or a closed section (such as a hollow structural section). I really think you need to refer to your design code, however here is how the NZS 3404 code tackles this problem...
Design Warping Normal Stresses f*w = Mfy/Zeyf
where
Mfy = Magnitude of Warping Moment
Zeyf = design elastic modulus for the one flange about the minor principle y-axis of the section as a whole
Zeyf ~ 0.5 Zey
Maximum Warping Shear Stress = TauW = (1.5 Vf)/Aw
where
Vf = Flange Shears
And combining these formulas normally requires the application of factors to account for second-order effects as well.
You really need to get a design quide on torsional design of open sections if you're going to check a channel.
Please see my attachment, which is a design procedure from HERA provisions and shows the Torsional design of solid, closed and open sections to NZS 3404.
Cheers,
YS
B.Eng (Carleton)
Working in New Zealand, thinking of my snow covered home...
You don't necessarily "need" to check a channel at all; I would definately try to get the load through the SHEAR centre, and please remember that this is a point behind the web (ie: falls outside the section). It is not the same as the centroid; There often seems to be confusion on this point when this subject comes up.
Cheers,
YS
B.Eng (Carleton)