After greeting

i have a design problem belong to the volume of hot water  to be supply for military dining facility .

I use the ASHRAE application hand book   table 9 hot water demands per fixture for various building to design the hot water volume for other building .

But this table does not include dining facility or restaurant. What is the other code demonstrate this hot water volume belong to dining facility


With thanks
 

RE: Hot water volume for dining facility

It depends on what type of dining facility it is.

If it is full service with full meals, I would suggest 2.4 gal/meals/day of operation.

If it is a sandwich/luncheonette, I would suggest 0.7 gal/meals/day of operation.

This is from The Unified Facilities Criteria which is used for USACE projects.

RE: Hot water volume for dining facility

(OP)
At 1st thank you very much for response  


Actually the facility provides three meals.


The hot water domain divided between the hand wash area for the troops and the kitchen service.  

That data you provide deals with gal/meals/day, is there a deferent data deals with fixtures. Like the sink and hand wash basin per gallon for dining facility?


 

RE: Hot water volume for dining facility

A dining facility would be considered a dump type load.  You would have heavy use for the 2-3 hours surrounding each meal.

To size for the handwash areas, you would size using the Table 9 you referenced.  I would probably use 4-6 gal/hr for each handwash fixture.  Depending on the type of faucet you use (0.5 gpm - 2.0 gpm) that equates to 3-12 uses per hour per fixture.  You might want to use the higher values since the fixtures would get used quite a bit.

Or you could add about 10% to your dining facility use and that would cover any additional fixtures.

RE: Hot water volume for dining facility

(OP)
Thank you very much for your response.
I shall use this quantity, hoping the VIAP consulting side gave an approved determination for the calculation.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources