Welding LATROFLANGE on Flat side of ECC.Reducer

Welding LATROFLANGE on Flat side of ECC.Reducer

Welding LATROFLANGE on Flat side of ECC.Reducer

(OP)
My question is If we (or is it allowed ?!)weld a Latroflange on to the Flat side of an existing 24"x20" ECC.Reducer in a LP Steam Line (DPr.& DTemp.:8.5 barg&290 Deg.C ), will the amount of SIF created(if significant) have a drastic effect on the integrity of the ECC Reducer?.Material for the RED is A234 WPB and the Latroflange A105.
Your replies will be greatly appreciated.

RE: Welding LATROFLANGE on Flat side of ECC.Reducer

pipeneer;
You should carefully review ASME B31.1 for this application. You will most likely need to run a stress analysis of this configuration and to check the area reinforcement in accordance with B31.1 to make sure that there is adequate reinforcement in the reducer because of this penetration.

RE: Welding LATROFLANGE on Flat side of ECC.Reducer

Yes, it is allowed but only after you've jumped through a couple of hoops first.

I agree that a stress analysis of the system would definitely be in order. However a reducer is a standard fitting according to B16.9 with standard SIFs. As soon as you make changes to the reducer, such as welding another fitting onto it, the standard SIFs no longer apply and need to be recalculated using a FEA program such as FEPipe. These calculated SIFs should then be used in the stress analysis. In the stress analysis it is important to know what piping code you are designing to. If your system passes the stress analyses then you should be home free.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources