ACI 318-05 appendix D Calculations with 2008 simpson catalog

ACI 318-05 appendix D Calculations with 2008 simpson catalog

ACI 318-05 appendix D Calculations with 2008 simpson catalog

(OP)
I am preparing  a master anchor bolt schedule for hold downs in the 2008 simpson strong tie catalog for single family residential. The design software provided by simpson does not do designs for epoxy bolts. Simpson provides an example calculation which follows ACI appen. D for the design of all thread bolts with set XP epoxy. While it is favorable to have any large anchor bolt cast in place at the time of pour, often the lack of skilled labor generates a bolt cast in the incorrect location and thus we must make a repair.
Hold downs with higher allowable loads when factored to generate Nua which must be less that PhiNsa, PhiNcb, and PhiNa, but since these are wood framed homes with 2x6 walls the concrete stem wall is also 6" which limits Camin to 3" which yeilds low bolt capacities none of which satitisfy the D4.1.2. I went back to check old designs for simular cases and per ACI 318 calc those no longer work. Is there truely no approved retro fit for an anchor bolt at a hold down along a stem wall?  

RE: ACI 318-05 appendix D Calculations with 2008 simpson catalog

No, Not with sufficient concrete strength to make the failure in the steel bolt as required, (unless small diameter bolt less than 3/8").   

RE: ACI 318-05 appendix D Calculations with 2008 simpson catalog

You can't use ACI 318 App D for epoxy anchors.  It specifically states in D2.2 that several types of anchors are not included in App D (and epoxy anchors is one of them).
Look in AC308

RE: ACI 318-05 appendix D Calculations with 2008 simpson catalog

StructuralEIT - Due to lack of guidance in the codes and the requirement of ICC approvals through much of the country (especially West Coast), Simpson and others are already using a version of Appendix D developed specifically for adhesive anchors.  This document (ICC-ES AC308) is the precurser to what will most likely be included in ACI 318-11.  

More background here:  http://www.structuremag.org/Archives/2007-11/D-Insights-Meinheit-Nov07.pdf

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources