STEAM LINE SIZING
STEAM LINE SIZING
I have what I think is a quick question. I have a currently installed steam heat exchanger that I want to double in capacity. Per the design data I am only using 1/3 of the exchanger's capacity (U=180 but I am only using U=53 BTU/(f^2*h*F)). As I understand it, to squeeze the additional capacity, I need only to increase my steam flow rate through the exchanger. I am currently supplying 300 lbm/h @ 60 psig and want to increase to 600 lbm/h @ 60 psig. I have a 3/4" supply line and a 1/2" condensate line. I though I would just need to increase my supply and return line sizes, but they appear to be sized correctly for the 600 lbm/h rate. Am I missing something? I don't want to mearly re-pipe to a bigger size without numbers to justify the work. Any input would be appreciated.
RE: STEAM LINE SIZING
Katmar Software
Engineering & Risk Analysis Software
http://katmarsoftware.com
Thew pressure drop is on an effective pipe length basis, not lineal footage so be careful.
The condensate removal design also needs to be checked.
Sometimes it just takes another set of eyes to inspire an answer.
Thanks for the help.
The condensate line is always of greater size than the supply line.
Offshore Engineering&Design
Would love to hear other opinions.
Using equation:
d(m)/dt= density (@ T&P) X Cross sectional area of pipe X velocity of steam, you can calculate velocity of steam and compare value with recommended values
Katmar Software
5,000 ft/min for heating service
10,000 ft/min for high pressure saturated steam
14,000 to 20,000 ft/min for high pressure super heated steam