Proportional controllable device?
Hey all,
I am brand new to this type of design, so this may be a simple question:
I am looking to add temperature and humidity control to an enclosure. The controls will be provided by another dept, I just need to spec the heating and humidification components. However all of these components have to be proportionally controlled - is there a way to know (other than calling the company) whether a heater or humidifier will work through proportional control? For instance, these heaters from Omega fit the power requirements I need, but I can't tell if they can be proportionally controlled:
option 1: htt p://www.st ego.de/fil eadmin/Bil der/PDF/En glish_US/H G140us.pdf
option 2:
http://www.omega.com/pptst/SREH.html
Can anyone with experience give me a clue, here?
option 1: htt
option 2:
RE: Proportional controllable device?
Your two choices can, specifically, be turned on/off as fast as you desire with NO issue at all.
Keith Cress
Both the units you've selected will self limit to some temperature. This means you can only turn down the heat using any of your methods from some maximum value these units top out at.
Keith Cress
For example you set up the controller to have a 10 second cycle time.
For 10% On 1 second Off for 9
For 50% On 5 second Off for 5
So you pick a heater that has more than enough capacity
The first example has built in temperature control, I think that would be hard to control, the second type is easier.
You need to tell the controls people that's what you intend to do otherwise they may supply a controller with 4-20 mA output, you need one with a solid state time duration output.
Roy
You can also use phase controlled SSR's but they can put more harmonics and noise on the power.